Drive ethernet lost communication (micrologix 1400/ panel view)
jimbob187jim
Jul 2013
mi
Have anyone ever had this issues
one of my machine lost comm from ML1400 to the pv
and gave a local pccc error 0x20 reading 1:1 from mircologix
I power cycle the ML and its back working.I still need to know what would cause this?:confused:
i'm adding picture of the com error
jimbob
An unplugged, damaged, or noisy Ethernet cable is the most likely reason for the disconnection.
You've also been posting about I/O module errors, and your facility is evidently a pretty inhospitable environment. If it were my system, I would spend some time improving the ground connections and the physical mounting of the controllers and cables.
For example, that MicroLogix you posted a picture of. There are little plastic covers that have been removed from both the serial ports, so because there are no cables plugged in, they're getting full of dust and other contaminants. When you finally do plug in a cable, you have a much higher likelyhood of poor physical and therefore network performance. At least get some electrical tape or foam rubber to cover those ports.
The same is true for Ethernet ports. Even ones that are plugged in are not really dust-tight. And I've seen a lot of Ethernet switches with unused ports that get badly contaminated with oil and dirt, then we plug in and wonder why we're getting network errors. Rubber plugs are widely available for RJ45 ports to keep the dirt out.
Now that I think about it, you were also posting about faults on the MicroLogix. Does this communication error occur at the same time as the fault on the MicroLogix ?
I am looking for some suggestions on good Ethernet/IP servo drives to communicate with an AB PLC. My customer has a non motion PLC but wants to...
1,195
Are there any documents that describe how to read/write (control) Invertek VFDs via Ethernet/IP from a ControlLogix PLC? If there are AOP (add-on...
2,316
Hi All, I am having issues communicating between an Omron CJ2M PLC and a Lenze SMV Drive (with Ethernet Module). I have set up Network...
1,158
Hi, I am trying to see if I can connect an Omron CJ2M-CPU32 PLC to a A1000 Yaskawa drive. My Yaskawa sales rep says yes with the addition of an...
2,508
I have a customer that has a Yaskawa Compact Vector v1000 with Ethernet, they want to add speed control and a barcode reader and speedup...
1,864