Simovert Master Drive -Profibus Enabling Running Problem
Engrtalha
May 2016
Pakistan
18
Experts!
Need Help
In My application i have Siemens CPU 316 WITH APPROX 28 PROFIBUS NODES (including Simovert Master Drive -14N.o.s & IM153 & Et200 Module).There are 02 Drives which are running with Single slection from HMI and drive were running normally for weeks but sudden 01 SImovert Master is creating Problem after Enabling.
Problem Detail:Normally drives shows P008
and after enabling one drive is running normally(5.4 Hz approx) while other is showing some values for 1-2 second on Drive Display & slight Motor Movement Physically then stuck or showing 0.000 on display ,mean while other drive is running normally.
Kindly guide me what would be the possible cause for this Drive response problem stuck on 0.000 while other Motor is running.
Task Atempted:Re parameterize drive again but status is same
Changed CUVC card -Reparameterize -Status same
Checked Profibus shield Grounding -OK
Checked Drive Power DC Link -OK -Motor Check OK
Plc status: normal no bus/Communication failure.-Online Status
Drive status Normal
Drive Model #:6SE7023-8TD61-Z
Communication card :CUVC + CBP +T100
Siemes CPU 316
Attached Simover Mster Drive Wiring Diagram
System Topology-Profibus nodes.
Can you swap the two motors and see if the problem follows the motor?
Or, swap the two drives and see if the problem follows the drive?
MadPoet.
Hi Dears, I am doing a project master drives CU2 To CuVC convertion. When I connect with Old Cu2 card with drive monitor it give me error...
1,488
Hi, i need to connect to a simovert VSD through profibus to compact logix 1769 l35E. What is involved in this process. do i need to change any...
2,408
Hi Drives experts, we have 32 Siemens master drives runing on profibus with S5 155U on Im308c. Now one drive 37Kw 6ES7027-2ED20 runing with CU2...
3,998
hi friends, we have master drive 6SE7026-0TD20 with DC unit 6SE7028-6EC85-1AA0. our inverter become faulty(6SE7026-0TD20). Question is Can we...
1,898
My Dear Siemens professionals Funny question may be but can anybody give me a clue regarding two different types of frequency invertors which...
5,033