Bruce99
Ive just come across a problem that Ive seen before. Upgrading a
PLC2-30 with four racks. All the ASB modules were set up ahead of time. Rack one, two and three are A4B 16 Slot. The fourth is an 8 Slot. I Pulled the comm modules and set the back-plane switches, installed the PLC5/40 and the ASB modules. Powered everything up logged in and did autoconfig. Rack one is the PLC resident rack configured as Rack one rather than the PLC5 default. (for addressing on the wires). Ive done this before without any problems, but this time racks one and four were OK, but racks two and three could'nt be configured as two slot addressing. I need all the racks set at two slot addressing or I've got a lot of rewiring to do. The modules are 8 point input and output, so I could replace them with 16 point modules, but rewiring 19 modules??? Ouch! One other time this happened and we ended up changing the rack. It solved the problem but what is with these switches?
Has anyone seen this before and what did you do to fix it? What can these racks be used for?
Special note:
These racks have plastic "locking" ID Tabs, not the metal rail on the top, above the modules. Rack two backplane switch is black in colour, and doesnt look like a repair job. I have never seen a black one before. Rack three is red, but the numbers on the switch are arranged backwards. The backplane calls position one on the top, on the switch one is the bottom. Open is labeled on the backplane as Left and closed is right. Because the switch is backwards, "open" is on the right. I used the backplane switch numbers and the label on the switch for the state, right being open. This didnt help.
I spent two hours changing these settings on both racks. I had to quit to put the PLC2-30 back in and test. Playing with these settings wears the switch to the point they no longer work.
My next step is to buy two new racks and preconfigure both the ASB modules and the racks. This means pulling all the modules at change over. Is there something easier I could do? Are these old racks now junk? No one wants to send them out to be repaired.
I love this job!!!
Any info would be gladly received.
Special note:
I love this job!!!