RSLinx OPT Test CLient Won't connect

RUSSRMATIN

Guest
R
Gentlemen,

I have just installed RsLinx for RS View version 2.42. I can configure an OPC topic and everything looks kosher, but my client will not connect to the RSLinx server. When I run OPC Test client, I cannot connect to the RSLinx server either. Has anyone seen this before? I installed this version, so I am led to believe I configured something wrongly. Any ideas?

Russ
 
RSLinx for RSView is a special license of RSLinx that will only serve OPC to an RSView client. No other clients can connect to it, including 3rd parties and the Test Client.

Is your OPC client RSView, or something else ?
 