cable needed
Do you have a serial and/or USB port on your PC?
What CPU of the SLC are you connecting to?
If you are connecting to a block SLC then you will need a DH-485 converter such as a 1747-PIC (for serial) or 1747-UIC (for USB).
If you are connecting to modular SLC CPUs such as SLC 5/01, 5/02 you will require the above.
If you are connecting to a 5/03 then can use a serial cable 1747-CP3 if you have a serial port. If only a USB port then you will need the 1747-UIC.
The 1747-UIC + additional leads would be a good investment for comms to all the above mentioned SLCs aswell as 5/04.
Download/view SLC literature at http://www.ab.com
rabbittgun said:
anyone know what cable i need for rslogix to slc500 for programming
What SLC do you use?
SLC5/01, SLC5/02 --- you need 1747-UIC (RS232/RS485) adapter
SLC5/03, SLC5/04 ---- you need standard null modem cable
If you are going into the DB-9 RS232 port a standard Radio Shack null modem cable will do the job.[/QUOTE]
To me it did not work on slc 5/05 and micrologix 1500. I cut it and converted to 235 i.e 2--3, 3--2, and 5--5. then it work well. so try both way. thanks
Thats a standard RS 232 pinout the Null modem pinout is a 2-2 3-3 5-5
[font=Arial, Helvetica, sans-serif]Common Null-Modem Connection[/font]​
[font=Arial, Helvetica, sans-serif][/font]
2-3 3-2 5-5
This is a null modem pinout
Hi all, A client has an existing pump house with a GE 90-30 PLC controlling things. I need to connect to it and extract the code and tags from...
2,530
Well, Bubba struck again, I am part of the IT department and we do all the plc programming. I will also add that all but 1 on the IT department...
1,700
We are trying to use 1492-AIFM8S-3 module with 1756-IF8I module. RA has a technical post "728767 - Wiring system solutions for 1756-IF8I...
1,273
Does anyone know the correct AB cable I need to connect a laptop serial port to an SLC 5/04 processor programming port, specifically the DIN...
13,314
Completed alot of .pdf's, Still unsure what direction to proceed. Want to use SLC/5/03 OS302 B Rev10.Channel-0 [DH485] [9-Pin] to SP10 Com-2 RS485...
4,791