DH485 Comm Cable SLC5/03 CH-0 Needed

JLDrescher

Member
Join Date
Jul 2009
Location
Georgia
Posts
13
Completed alot of .pdf's, Still unsure what direction to proceed.
Want to use SLC/5/03 OS302 B Rev10.Channel-0 [DH485] [9-Pin] to SP10 Com-2 RS485
SP10/Interact [6.1] Program Completed, Interact Shell Installed incl Tag Editor Descriptions All Verified,
SP10 Is Showing Programmed Screen's.
Using CTC/PS10 Description Format: ABDH\1$B3:0,0 ,ect

CTC Set For Com-2, RS485, ABDH Driver, SLC5 Box Checked.
Not Sure w/SLC5/03 DH485 Cable Wiring ???
So far SLC5/03 CH-0 [RS232 LED Indicator Is Blinking] w/DH485 Protocol Setup.
1st Time Doing a CTC/Interact HMI.
Any Suggestions/Comments Really Welcomed.

UPDATED: 07.09.2009
Verified PS10 Com-2 Jumpers RS485, Attached File Is All I Found
To Date w/CTC&AB, AB's Pinout's Description's Not Matching CTC's
Pinout Description's. Not Sure How To Wire a Cable For RS/DH485
At This Time.
Thank's



RS485 to DH485 RJ49.JPG
 
Channel 0 on any SLC-5/0x controller is only an RS-232 port.

It does not have any sort of jumper selection that switches in RS-485 or RS-422 wiring. The selection of DH-485 protocol only changes the protocol, not the signalling.

You should change the jumpers on your CTC terminal serial port to RS-232, and follow the RS-232 wiring diagram to connect to Channel 0 of the SLC-5/03 controller.
 
Thank's Ken,
I Do Have That Info, Will Go For The RS232 Cable Wiring ASAP.
Any Thoughts About SLC5/03 CH-0 Set Up, ie: DF1 Full/Half Duplex,ect.
I Do Know The Baud,Parity,Stop Bits Have To Match as Well As IRQ's
On Both End's. Not Sure About Selecting DF1,ect Though, Memory Serves
Me, DF1 Requires "MSG" Rung Logic.
Thank's Again Ken
 
In virtually all HMI applications, the HMI device performs all the communication requests. MSG ladder logic instructions are not required.

Configure Channel 0 of the SLC-5/03 to match whatever you configure the CTC panel for.

If you set up the CTC panel for DF1 Full Duplex at 19200 baud, 8/N/1, no handshaking, it will match the default settings of the SLC-5/03.

I have never used a CTC Interact product and I cannot tell you anything about their communication settings.
 

Similar Topics

Hello experts! So I'm migrating old PV600 RS-232-DH485 (2711-K6C5) communicating to ML1500 LRP to a new PV+ 700 (2711P-K7C4A8). I've...
Replies
1
Views
1,386
Hello experts, There's an existing PanelView600 (2711-K6C5 which has only RS-232-DH485 communication port) communicating to a MicroLogix 1500 (it...
Replies
35
Views
15,407
I have a G306 hmi I have tried to upgrade from a panelview 600 on an existing line that is connected to a SLC 5/03. I have had succuess for the...
Replies
7
Views
2,589
Hello all. I would appreciate your help in troubleshooting an AB multi-drop DH485 network. Our company was retained to modify existing machinery...
Replies
2
Views
7,303
Have a CTC/Parker PS10 Model HMI, Going To Use Comm-2 [RS485] On PS10, Configured w/ ABDH SLC5/1 Network Driver. [Interact Shell Installed] Allen...
Replies
0
Views
4,577
Back
Top Bottom