Controllogix Module, Reading the configuration
asterof
May 2007
Califonia
554
Anyone know if it is possible to read a analog input modules
configuration settings, such as the engineering units
using a GSV or some other instruction
All the configuration settings are already created as Module-Defined Tags in the Controller-Scope database.
For a module in Slot 5, for example, the Configuration data is stored in "Local:5:C"
Changing those values in logic does not apply them to the module; you need to perform an "Apply Configuration" service using a MSG instruction to programmatically reconfigure a module. Look for the topic "Reconfigure an I/O Module Programmatically" in the online Help file.
Eddie is correct about accessing configuration data through the local tags.
I use a first pass configuration routine to configure all analog modules when the program first starts. I have to disagree with Eddie in that I never use a MSG instruction to apply the changes to the modules. I have had success modifying the module configuration through logic without using a MSG.
Not seeing them
All I need to do is read the high and low engineering
values. I do not see those in the processor tags
I see filters and such, but not the engineering values.
A I missing something
PS.
too many narcotics when I was young, I forgot to turn them on in the
Show All Checkbox's, However the information you supplied did educate
me to some abilities I never knew existed.
Thanks a bunch
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
84
When adding an IFM AL1322 IO-Link Master Module to a 1756-EN2T Ethernet Card on a 1756-L82E Controller, The Input and Output data file does not...
105
I am building a ControLogix network with about 70 nodes. I was going to use a 1756-EN2T. Until I noticed that the 1756-EN4TR has way more...
2,088
I've worked on a handful of projects that relied on a Prosoft module for Modbus comms with other systems (older PLCs, boilers, chillers, much...
2,152
Hey everyone, ran into something I've never seen before and was wondering if anyone had any idea of what's happening. Currently in the middle of...
2,054