Pass Through with PanelView and Micro820?
m0t
Jul 2013
Illinois
I am new to Rockwell stuff, have more experience with IDEC.
I was handed a half completed project using a Micro820 and a Panelview 2711-T2T. There is an RJ45 cable connecting the 820 to the HMI panel.
I want to know is there a way to connect to the panel and "pass-through" to program the PLC? With Idec we did it like that. I would have to use the one of the serial connections on the HMI to connect to the PC? How to set that up? Thanks.
Or pass thru the other way, from the 820 to the Panel? Or connect the panel to the 820 via serial?
Thanks.
Welcome to the PLCTalk forum community !
Can you clarify that PanelView part number ? A small PanelView 800 would be a 2711R-T4T.
Both the Micro 820 and the PanelView 800's use an RJ45 connector for Ethernet, so your system designer probably decided to over-simplify and connect them point-to-point, to save on the cost of an Ethernet switch and require you to connect a switch while commissioning, or to connect to each device individually.
I'm not aware of a port-to-port bridging or pass-through connection on either of those devices.
Thanks for your reply. Yes it is a 2711R-T4T. I think there is a way to connect the panel and the PLC serially and use the ethernet for download but they still would have to be programmed individually.
Yes, you can connect a PanelView 800 (DB9 serial port) to a Micro 800 (terminal block serial port) for runtime comms, but download to them separately over Ethernet.
The CIP protocol supports "bridging" between ports, but I don't think these low-end devices can do that he way the ControlLogix can.
I've been given a line that has several sysmac c200Hx PLCs. The First station Im trying to wrap my head around has a NS8 HMI. I'm using Cx-one...
758
Hello, I have a Panelview Plus 1000 that I have setup to trend historical data. It works fine, however I would like to use the same trend screen...
1,254
Hi everyone. My plant's about to move some equipment to our sister plant and I've been asked to take some back-ups of the PLC and HMI programs. I...
1,963
I replied to an earlier post with this scenario but decided to start a new thread in the hopes someone has tried this before. I have been...
1,752
Hi all, I have multiple Allen Bradley SLC5 PLCs on my site, with most of them having a DeviceNet card installed. Each PLC also has an Ethernet...
2,386