Actuature AME 110 NL

Join Date
Jun 2012
Location
Saudi Arabia
Posts
14
Hi Buddy!
I have Actuature AME 110 NL ( 082H8057) its power is 24VAC . and its control Voltage 0..10VDC. and it has 3 wire (Red 24VAC, Y Control Signal, and Common). really I don't know how to link to the Analog Out module from Siemens (6ES7 135-6HD00-0BA1). what shall I connect to Common -0..10VDC / -24VAC. please advise the proper connection and thanks in advance.

WhatsApp Image 2020-03-23 at 13.40.49.jpg
 
It looks to me that you need to connect the common of the 24v ac to the common of the analogue output (could be -VE or Com or OV) so in effect the common of the 24v AC supply will be connected to the ov (com) of the analogue output I must admit it is unusual to see a 24v AC supply.
 