I have an Allen Bradley 150 SMC Flex that I need some help with.
I have it set up with a 20-COMM-E card over ethernet back to my control logix PLC.
I get my Enabled bit for Control Power being ok back to my PLC as well as my phasing active.
On the drive lcd screen it says stopped where it shows the Volts, Amps and MTU.
If i reset the drive in drive explorer i get a comm fault and i can reset that fault from the PLC using the ClearFault command.
When i send the start signal nothing happens though.
Is there a setting I am missing somewhere? We also dont have a motor hooked up to the drive, one of the guys thought that might be why, but i should still be able to run the drive should i not?
Any help on this would be greatly appreciated.
Thanks,
Dennis
Do you have any of the discrete I/O connected ?
Even if you plan to run the drive entirely over the network, you still need jumpers on the Enable and the Stop terminals or those will over-rule the network Start command.
Check out the Typical Wiring Diagram on page 3-13 of the User Manual.
Ken,
Thanks for the response.
I did figure shortly after posting this question. It was the wiring. I didn't have pin 16 an 18 jumped with pin 11. Once i did that it worked.
Thanks,
Dennis
I need to purchase a few Large soft starters for our plant and we prefer to stay Rockwell. We have purchased SMC Flex 150 in the past and they...
411
Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
357
Hey When i am adding 150 smc flex to the project, i need to change "Drive Rating", what is drive rating? I tried with help but still, cant...
1,594
Hello, I would like to start the SMC without load. How can I desactivate the fault 40 : no load thank you for answer
4,399
Hello Friends, I am using about 30 number of 150-SMC-Flex devices on DeviceNet with 20-COMM-D Series-B module. I have installed the modules and...
2,431