SMC flex 150 no load
You can't. All soft starters use SCRs as the power devices. An SCR works based on current flow. If there is no load connected, there can be no current flow, so nothing happens. There is then, in essence, no way to "run" a soft starter without a load, it NEEDS a load in order to "run". What you can do however, if you want to test functionality, is to connect ANY load to it; a small 3phase motor, a resistor bank, even 3 banks of light bulbs (with enough in series in each phase to lower the voltage to each bulb to its rating). Then you will run up against the "Under Load" protection, but that can be disabled in programming at Function 51 by setting it to zero.
SMC flex no load trip
Function 51: Setting is for underload tripping but
Fault 40: is no load tripping.
underload is Fault#23
no load is fault#40
Hence how to avoid no load fault
Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
314
Hey When i am adding 150 smc flex to the project, i need to change "Drive Rating", what is drive rating? I tried with help but still, cant...
1,570
Hi All, I have an Allen Bradley 150 SMC Flex that I need some help with. I have it set up with a 20-COMM-E card over ethernet back to my...
4,968
Hello Friends, I am using about 30 number of 150-SMC-Flex devices on DeviceNet with 20-COMM-D Series-B module. I have installed the modules and...
2,404
Hi there, very much new to AB Drives / Drives in general. Driving a pump with SMC Flex Drive Rating: Pump (5-135) Revision 6.008. Currently the...
2,162