s7 300 to simoreg
SHYAMAL
Aug 2007
DHAKA, BANGLADESH
53
If I want to send 6 words (PPO4) from PLC (CPU 314 C– 2DP) to the drive (SIMOREG) over profibus with SFC15 (1st word for control word), then does the 1st word have bit to bit direct correspondence to the control word?
As for example, whether bit 0 of the 1st word corresponds to bit0 of control word of drive, bit1 to bit1 of control word of drive and so on or it corresponds reversely.
Please help.
Shyamal
Dear LD,
Thank you very much for your immediate response.
For a specific case, if I have the word 0100 1001 1101 1011 in PLC and send it to the control word through SFC15, will the control word look:
Bit15 = 0, Bit14 = 1, Bit13 = 0, Bit12 = 0, Bit11 = 1, Bit10 = 0, Bit9 = 0, Bit8 = 1,
Bit7 = 1, Bit6 = 1, Bit5 = 0, Bit4 = 1, Bit3 = 1, Bit2 = 0, Bit1=1, Bit0 = 1
Say, from a function block I am calling SFC15 with the following code:
CALL "DPWR_DAT"
LADDR :=#Drive_Address_HEX
RECORD :=P#DIX 16.0 BYTE 12
RET_VAL:=#Ret_Val_Error2
And say, the word DIW16 has been referred with the data mentioned in my second post to the control word of the drive.
DIX bits map to the drive control word as follows:
DIX16.0 = Drive Control word bit 8
DIX16.1 = Drive Control word bit 9
DIX16.2 = Drive Control word bit 10
DIX16.3 = Drive Control word bit 11
DIX16.4 = Drive Control word bit 12
DIX16.5 = Drive Control word bit 13
DIX16.6 = Drive Control word bit 14
DIX16.7 = Drive Control word bit 15
DIX17.0 = Drive Control word bit 0
DIX17.1 = Drive Control word bit 1
DIX17.2 = Drive Control word bit 2
DIX17.3 = Drive Control word bit 3
DIX17.4 = Drive Control word bit 4
DIX17.5 = Drive Control word bit 5
DIX17.6 = Drive Control word bit 6
DIX17.7 = Drive Control word bit 7
Thanks LD
I have one more question if second PZD word is spindle feedback then how it is? Is it floating point format or other ? How to convert it to real?
If the drive is configured to send back one word representing the spindle speed, then it will be a signed integer where 16384=100% speed.
To convert to real use:
L iSpeed
ITD
DTR
T rSpeed
27
Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...