Good Morning ,
We had a 3 phase motor go bad yesterday . The motor had no nameplate .
How can you determine what RPM ( or how many poles ) without a nameplate .
Any links or videos ? Good teachable moment yesterday.
Thanks so much in advance .
There MAY be just a little bit of residual magnetism left in the rotor bars from the last time the motor ran. If you get a scope and hook it to two of the motors leads and spin the rotor at a known-ish speed you may be able to determine the pole count from induced voltage at the motor leads.
Or you could try to get a feel for what the driven load speed was and work it back through the drivetrain. You aren't looking to be exact; you just need the pole count.
Keith
RPM = (120*f)/p
f = frequency of line
p = number of poles per phase
Example - 3 phase motor with 24 poles connected to 60Hz line
24/3 = 8 poles per phase
So
RPM = (120*60)/8
RPM = 900
RPM = (120*f)/p
So
RPM = (120*60)/8
RPM = 900
Just to add to this a bit, when you get a motor that is 1750RPM, that just means they are adjusting for the slip in the rating and that zero slip would actually be the perfect 1800RPM of a 4 pole motor.
RPM = (120*f)/p
So
RPM = (120*60)/8
RPM = 900
But with no nameplate, you don't know the number of poles...
If you knew what to look for in a stator, you could disassemble the motor and dissect the coils to see how many poles it has per phase by looking at the coil groups. But that's not easy to do for the uninitiated. This will give you some idea of what that might be like.
https://www.easa.com/resources/software/how-wind-three-phase-stators
Do you have reason to believe that the RPM is something other than 1800 or 3600? If so, Kamenges idea of backtracking through the drive train is the way to go. If not, a gearbox connected directly to the motor may have a max RPM rating that would point to the answer.
Is the motor driven by a VFD? If so, the parameters in the VFD may shed some light on the problem.
Oh definitely! It was a little easier to do on the trainers in trade school where you could clearly see into the motor.
Without a nameplate, how do you know required HP for your replacement motor? It seems RPM might be only part of your problem.
Relying on frame size alone isn't a good idea; multiple HP ratings are available in each frame size, and oversizing may be as detrimental as undersizing the replacement.
-rpoet
You might be in a situation where it will be easier to reverse engineer the application. Whatever the motor is/was driving has requirements that the motor satisfied so if you start there (I.E. how fast does whatever the motor was driving need to run, what kind of power does it take to run it, etc...) it may be easier to spec the replacement motor rather than figuring out what the old motor was.
This! It's like broken belt on conveyor. If you can't find the length when you can measure it
Do you know the kW rating of the motor? You might be able to have an educated guess by looking at the motor over load setting.
I say this because if you know the know the kW rating and you can measure/calculate the frame size, then you could possibly find a table that shows you the number of poles
I found this on the ABB website... Too easy if it is a 90L frame..🍻
We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
113
Hello, i am a beginner with a Siemens Logo 8 PLC. I would determine the direction of an object if it passes a whole cycle of 2 input sensors. See...
227
Hi all, Just looking through the CIP_AXIS_DRIVE data type in a Logix controller to look for something that can tell me whether the current...
1,115
I'm currently working on an MES interface PLC which passes around a whole bunch of strings. A lot of these strings are really just to allow for an...
1,140
I don't use AB much these days, and any installs I've done in years past have been setup by myself from scratch, so I've always known what...
2,133