Citect SCADA - Supergenie ?#? Any Limitation?

What version of Citect?
I ask because if it is 7.2 then you don't need to use numbers you can use text eg ?running? Makes it all a lot easier to read
Not sure what the limit is, but if you use the A s s function you can keep adding more, Ive got to about 40 with no problems
 
I remember that some where in the documentation it mentions that we can pass up to 255 parameters to a supergenie pop up page. If you are using A s s w i n function, maximum eight parameters only can be passed. if you want to pass more than 8, use A s s function to associate variables one by one and then call A s s p o p u p function
 
What version of Citect?
I ask because if it is 7.2 then you don't need to use numbers you can use text eg ?running? Makes it all a lot easier to read
Not sure what the limit is, but if you use the A s s function you can keep adding more, Ive got to about 40 with no problems

Mind telling more of ?running?
I'm currently using ver7.0 on project purpose.
We have the ver7.2
 
I remember that some where in the documentation it mentions that we can pass up to 255 parameters to a supergenie pop up page. If you are using A s s w i n function, maximum eight parameters only can be passed. if you want to pass more than 8, use A s s function to associate variables one by one and then call A s s p o p u p function

Thanks, now I remember I read stuffs like that, 255 parameters.
I've found out about the adding stuffs, but it's kinda troublesome I thought, to individually assign up to a huge number of parameters as of the original 8.
 

Similar Topics

I am trying to display a variable within a cicode function onto a graphics page. This function queries a SQL database. I can get the value onto a...
Replies
3
Views
288
We are trying to set up a newer generation Omron PLC (NX/NS Series) with Citect / Aveva Plant SCADA using the Ethernet/IP CIP Protocol to read...
Replies
2
Views
358
I am new to Citect SCADA and I am building the graphics for a page that will contain the control of a plant by a Kingfisher RTU. The project I...
Replies
0
Views
266
Hi All, I aim to use Aveva Plant SCADA 2020 to read and write data from/to Omron CJ2M CPU35 PLC using OMFINS protocol. However I have Bad Data...
Replies
1
Views
727
Hey, I'm trying to do the following, I have some experience with Citect but can't seem to figure this out. I/O Tag: BoxPos1_ProdNum (Data Type...
Replies
0
Views
579
Back
Top Bottom