MicroLogix 1100 MSG to SLC 505
bro08170
Aug 2006
Utah
I am trying to route I/O info from a ML1100 to Wonderware suitelink through a SLC 505 (because Wonderware forgot the ML1100 has told me they don't support it). I don't have lots of info to transmit, so I am trying to route it to another SLC 505 on the Ethernet Network (and thus, into Wonderware).
I have tried using a MSG read command in the SLC 505 logic, but it isn't reading the data from the ML1100. Any ideas or tricks for this one? (is the MSG command somehow different for the ML1100, even though they both use RSLogix500)?
Did you choose "multi-hop", if not, do so.
Select multihop near the bottom of the MSG instruction, then click on the multihop tab at the top and enter the IP address of the ML1100
Do the Multi-Hop
That worked. I should have followed my intuition- I was going to try it, but I didn't want to be chasing my tail.
Thanks!
The 5/05's support two ethernet protocols, the old CSPv4 which allows it to communicate with the older PLC-5's etc.. and the new EtherNet/IP which is what the ML1100 uses. When you select multihop, you're telling the 5/05 to use the new protocol, if multihop is not selected the 5/05 will use the older protocol.
I would have added this earlier, but I was pressed for time.
Helo everyone! I am using micrologix 1100, for communicate through Ethernet IP whith 4 weighing modules, 3 of then are comunicate properly...
774
Hello All, I have a total of (8) prox switches that I am monitoring (1 for each machine) with a single MicroLogix 1100 controller. I have (8)...
5,249
Dear all, I am testing MicroLogix 1100 to read from SLC. In SLC there are 10 tags (starting from N51:20) that I need to read in MicroLogix. So...
3,620
Hello all, I have a MicroLogix 1100 Series B that I am trying to read data from and into a PLC-5/20 Series D Rev A. I assume this is...
3,692
Hey, I have a Micrologix 1100 and I am sending 6 messages to a Yaskawa VFD, both reads and writes. I can't figure out how to build logic to have...
1,706