Code 16#0113 Connection request error: Module connection limit exceeded
matatata
Aug 2017
Croatia
32
Hello
I am working on a furnace, it has a decent amount of I/O. I've tried to add some kind of recorder to my system but im getting this message :Code 16#0113 Connection request error: Module connection limit exceeded:. I've tried connecting recorder to other communication card that was empty but still had they same error, i tried increasing RPI, but no luck. Cards in question are 1756-EN2T.
Before posting here i tried to look on rockwell support and here, but this problem isnt that often.
What kind of recorder ?
Is this a Rockwell device, or a device with an Add-On Profile, or a device with an EDS file, or a Generic Ethernet device ?
While all of those use the same protocols to establish an I/O connection, they get their configuration information in a different way, so the diagnostic methods might be different.
In general that error code will be reported to the ControlLogix when it tries to make a connection to a device that doesn't support multiple connections, or that doesn't support the type of connection you're trying to make (like a listen-only or a Redundant connection).
6180 Aerodaq recorder - in the manual for the recorder, there is a guide for connecting it with allen bradley plc. im using a generic ethernet device as instructed by the manual.
Thanks for that information.
Can you point to the Aerodaq RSLogix 5000 example code or reference manual ?
Does the Aerodaq module have an existing connection to another controller ?
Is it simultaneously connected to another software package ?
Are you also sending MSG instructions to the Aerodaq module ?
Do you have the Aerodaq module in the I/O tree via more than one 1756-EN2T module ?
In general, this error code really does mean that the Aerodaq module is rejecting the connection request because it thinks its connection resources are used up.
- Manual in question from Page 199 - https://www.eurotherm.com/index.php?route=module/downloads/get&download_id=151
- No, it is connected to stratix 9000 which is connected to a plc
- No
- Im not sending anything, i've just tried to add it to my I/O list and i get this error
- Dont understand this question, i added it to a 1756-EN2t module once, if that is your question.
- Ok, i will try to check recorder a bit more
quote
Ken Roach said:
...In general, this error code really does mean that the Aerodaq module is rejecting the connection request because it thinks its connection resources are used up.
Hi Ken,
From memory, I think the error code might be referring to the connections in the 1756-EN2T modules as being maxed out, and not the recorder module itself?
The 1756-EN2T has available 128 TCP and 256 CIP connections. I definitely know that because I have one in a project in front of me now. Whether this recorder module is actually tipping the EN2T modules over their connection limit or not, would require us knowing more about the existing I/O Configuration. If it did, it means both the tried EN2T modules must already be heavily loaded, else the generic module configuration is throwing some crazy numbers at them?
Regards,
George
I checked the recorder further and was able to enable communication and now it works fine, thanks for this tip. o_Oo_O
Welcome to the PLCTalk forum community, BTJ.
It would be preferable to start a new thread for your RFID reader, especially since the solution to the original problem was specific to enabling the EtherNet/IP comms features of the data recorder.
Go to the main Q&A page, and click the green "Start a New Thread" button.
Post the type and revision of ControlLogix you're using, and some details about the RFID reader.
In general, the 16#0204 error code indicates that the device can't make an EtherNet/IP I/O connection at all. Often that's because the device isn't communicating on the network at all (it's disconnected or not at the correct IP address) or it means that the EtherNet/IP protocol is not supported or is not active on the device.
PING is the first tool you should use, but I really like TCPING (www.elifulkerson.com) because you can specifically test a connection to TCP Port 44818, which is used by all EtherNet/IP devices.
Hello, I have a problem with control logix. Using "1756 controller", 1 "1756EN2T" ethernet module, and 2 "1756CNB/E" controlNet modules. I...
5,324
I am trying to communicate with an Acromag 951EN-6112. I have a Compactlogix 1769-L36ERM I have loaded the EDS file for the acromag I have...
1,225
230
hello, I'm a student and for my final grade I have to repare a sepro robot. the only problem I have for now is that i have an error code 3...
35
I received an email from a student with the following code attached. This is supposed to control a floodgate system, and supposed to be written...
23
780