I have been asked to get as many parameters as possible out of powerflex 70 Drive and show it on HMI. Can I get some tips or help how to get most number of parameters?
Are you trying to get the parameters directly to the HMI or through a PLC?
You can get 8 parameters using Datalinks from the PF70 to the PLC, standard you will get the speed feedback, then you could use messaging to get any more parameters that you desire.
Alan
Create a message to read the parameter, you will need to read the manual to see how to set up your message instruction (what tag you need to read, some drives use the N registers)
Alan
So you have a 20-COMM-E in the PF70?
Yes. I have a 20-COMM-E in the PF70. I tried to search for it in the manual but it does not explain anything about the messaging method
Native tags when added to the IO
If the drive is connected using ethernet and has been added to the Controller Orgnizer tree then all the parameters are
listed as native tags. Add the drive as an object to the I/O Configuration section. Try it off line you will see what I mean. While the 400 plus configuration are not all there the entire status and setup parameters are. Once added make sure you SHOW ALL TAGS in the filter
This is my university project. the project requires to use Factory Talk View SE and RSLogix5000 to control and monitor many important parameters remotely.
and also create faceplates to be used for multiple instances of the monitoring and control of electric motors allowing a simple re-usable system
what do u reckon about this project Alan?
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
158
I have a client who's Powerflex 755 VFD has one of its inverter cards failed. the card is with the model number SK-R1-IG1-C770D740. Does anyone...
269
Is it possible to set IP address of Powerflex drive, without powering up the entire 3 phase circuit? Is there some way to just power up the keypad...
731
Hello, I have a machine with 4 powerflex 4m drives that are networked using a 22-XCOMM-DC-BASE with a 22-comm-e card attached. Backstory....There...
480
Hey all, I wanted to discuss an issue with achieving a constant flow rate of around 10 GPM on a glycol circulation pumps in a 1200-1300 PSI...
976