Hello ppl,
I would really appreciate it if someone can send me a sample program for GeFanuc series 90 PLC. What I need to do is..I'm taking input from a pH electrode and if the pH reading is below a particular value say 8 , I want to switch a relay , if it goes above it i want to switch it off again! If you kant give me the sample program, atleast give me an idea how to do it.
Thanx, waiting for your reply,
SSS.
 
There are six relational instructions in the Series 90-30 function set. They are GT (Greater Than), GE (Greater Than or Equal To), LT, LE, EQ, and NE. They compare two numeric values and turn on or off a discrete bit depending on the results of the comparison. These will do what you need.

Your pH sensor will report a value to an analog input channel (%AI). The raw data from the analog channel may need to be scaled before using it in the comparison instruction. For example, maybe the pH sensor transmits a 4 - 20 mA signal to the analog input module such that 4 mA represents a pH of 2 and 20 mA represents a pH of 12. The raw data in the analog input corresponding to 4 mA is zero, while the raw data corresponding to 20 mA is 32000. You will need to perform some arithmetic to scale those raw data values to engineering units (pH).

Depending on which CPU model you have, you may be limited to performing arithmetic calculations on integers.

I hope this points you in the right direction.
 

Similar Topics

I have an old PLC (circa 2007) consisting of Telemecanique/Modicon/Schneider Electric devices. The system has developed errors and unfortunately...
Replies
2
Views
230
Guys, please help me with this urgently. We have Logic 5575 installed in hot n standby setup. For some reason, the primary now cannot sync with...
Replies
10
Views
379
I have DI module ICPCon M7024UD connect to my pc using COM3 MODBUS RTU and also RHT sensors are using MODBUS TCPIP.. The problem is, it cannot...
Replies
9
Views
1,668
Hi all, We are facing synching issues with redundancy module, where the Primary is ending up with disqualified secondary. Normally this would...
Replies
2
Views
625
I have the logic of OMRON but I want to do this logic in TIA 15.1 CPU 1200...
Replies
4
Views
1,836
Back
Top Bottom