Looking to purchase a Profibus Diagnostic Meter... Any Suggestions?
lunenburger
Jul 2008
Summerside
209
We have multiple Profibus networks, some are on a Controllogix 1756-PFB-CLX card. And some are connected to a Siemens S7-300 PLC.
Just wondering if there is a preference on a good diagnostic scanner for these two networks.
The number of problems that got blamed on the Profibus networks in a factory I work in went down by half once we got a Profitrace unit:
https://procentec.com/products/profitrace/?content-1
Some of that is because we now have a very powerful and precise tool to track down bad signals, bad connections, and bad devices, so we've fixed a few of them and know the characteristics of the intermittent ones.
And some of it is because now the network isn't mysterious; folks know we can exclude the network as the source of the problem and are more willing to pursue end-device, power supply, and system operational reasons why something doesn't turn on when they expect it to.
+1 here on the ProfiTrace, can vouch it is a very good tool.
I can also recommend the ProfibusScope software however it does not got into so much depth as the ProfiTrace. To use this software you will need a siemens interface card such as the CP5512 (this is what I use in my toughbook).
Regards
Daniel
I can only recommend Profitrace as I use myself. Quick to find fault cause and where the problem is.
I have used it with several customers, where they have abandoned themselves to find the error and where my Profitrace could quickly find it.
We used a Fluke Scopemeter when we were having ModBus difficulties, the new model does Profibus too among a few others, very useful tool all round if you haven't got a scope either:
https://www.fluke.com/en-us/product/electrical-testing/portable-oscilloscopes/fluke-120b
Out of curiosity I looked through the specs and the manual. In the manual it just says:
"Profibus - DP PA - EIA-485 61158 type 1"
Nothing more, in the entire manual.
I am guessing it merely checks for if the waveforms are withing the limits.
Profitrace does much more than that.
edit: Yes, that is what it does:
The Test Tool can indicate the status of the following
aspects of the OSI model Physical Layer:
• Voltage levels (bias, high level, low level)
• Bit width – baud rate
• Rise and fall time
• Distortion
Do you have a similar experience with Ethernet networks? Any recommendations on tools/tool features that you use often for commissioning and troubleshooting Ethernet?
That's funny, I did the same thing.... CTRL-F and 2 hits on the word Profibus
I have received pricing for the Profitrace.
there are two options, the Profitrace Pro and the Profitrace Plus
the Pro is $1700 more but includes PA Probe for measuring PA networks
There is a device called a Unigate CL-PBDPV1 I am not sure of its function other than it's a protocol converter.
Also, there are around 30 devices on the Profibus network including pressure and flow transmitters.
How do I know for sure if I have a PA network?
Help! Europe companies seem to be shut down during the month of August. Trying to find someone in the USA that Distributes ESA displays. Trying to...
2,676
Hi , Where i can find Mitsubishi PLC Card end of line & replacement model details. i am looking for Q02CPU replacement model. Please advice. thanks
126
I have Allen Bradley plcs, I have had Circuit breakers and other automation equipment in the past. There's no solid buyers local. How much do you...
204
can anyone has a good program to learn plc programming online. i have the basic looking into improve my skills thanks
144
I want to monitor a couple signals in a place where there is no PLC but there is ethernet. I know I can use an AENTR or Flex I/O and a module but...
21
785