Hello All,

i have scadapack 575 and i am trying to scale bidirectional flow meter. However my negative value from flow meter is not scaling. Any help would be appreciate. Below is my ST program.

EU_ir := (((AI_ir - MinAI_r) / (MaxAI_r - MinAI_r)) * (MaxEU_r - MinEU_r)) + MinEU_r;

MinAI := 0.0;

MaxAI := 1000000.0

MinEU_r := - 1500.00;

MaxEU_r := 3000.00;
 
See txt. Its a little different then your formula.

(((Scaled Max-Scaled Min)/(Max Raw Input-Min Raw Input))*(Raw Input-Min Raw Input))+Scaled Min = Scaled Value



MinAI := 0.0;

MaxAI := 1000000.0

I'm not familiar with your 575, is the above raw data values?
 
Last edited:
Hello All,

i have scadapack 575 and i am trying to scale bidirectional flow meter. However my negative value from flow meter is not scaling. Any help would be appreciate. Below is my ST program.

EU_ir := (((AI_ir - MinAI_r) / (MaxAI_r - MinAI_r)) * (MaxEU_r - MinEU_r)) + MinEU_r;

MinAI := 0.0;

MaxAI := 1000000.0

MinEU_r := - 1500.00;

MaxEU_r := 3000.00;



  1. What do you mean by "not scaling?"
  2. What is the raw Analog Input value (AI_ir) that is not scaling?
  3. What value of EU_ir do you see with that value of AI_ir in 2 above?
  4. What value of EU_ir are you expecting to see with that value of AI_ir in 2 above?



Also, it may not matter after the first scan, but I would put the Min/Max assignments before the the EU_ir calculation.
 
What is the analog input (0-10V/4-20MA) actually reading? Is the meter setup correctly to allow reverse flow?
 
Analog is 4 to 20ma and yes flow meter is set 4ma to -1500 and 20ma to 3000 and in flow meter itself when flow is negative i can see negative flow on flow meter.
 
Doesn't the Scadapack have a scaling instruction? Have you tried it?

The raw counts I see for an on board analog input are 0-10000 ( not 0-1000000)

SCAL
 
Last edited:
Are you using DNP3 to get the value back into GeoSCADA? What is the data type configured for the point in RemoteConnect? If you've got a UINT datatype for logic then you'll never see a negative get passed back to the DNP layer.

I would go online with the RTU and see what value you're seeing in the logic, and make sure that's showing a negative correctly. Then read the object / point using RemoteConnect. Does it match what you see in the logic? Then finally, if that is all correct, then I'd check my point configuration in GeoSCADA ( not familiar with it so I'm not sure if there's much to set up).

ZIP your RemoteConnect configuration and upload it here and I'll take a look.
 
So On Geoscada whenever flow is positive i get data on screen but whenever flow is negative i got zero value




Does the flowmeter have a display of the measured value? If yes, when the flow is positive, do the flowmeter's measured values agree with the Geoscada measured values?




Also, I noticed that the ST uses MinAI as the variable name of the minimum analog input, but the EU_r formula uses MinAI_r. What is MinAI_r?
 
Thank you guys for the help. Scaling was done correctly on scadapack it just on GeoSCADA DNP3 point zero scale value needed to change from zero to negative value.
 

Similar Topics

Hi People, I have a ScadaPack 330E that has been sitting on a shelf for a few years (previously working), and have recently re-installed...
Replies
4
Views
1,798
I've got 16-bit data at address 40200 on a Schneider Scapack 350. I can grab the data over Modbus TCP using Kepware at IP 172.16.1.100. When I...
Replies
8
Views
2,494
Hello, I’m still a novice when it comes to plcs, and I’m currently facing a problem I need help on. I’m on site at the moment, and connected to...
Replies
2
Views
1,522
I am programming a SCADAPack 350 with Telepace Studio. I want to know if the logic in running the first scan and if the program is running...
Replies
0
Views
1,254
Hi! I've got a customer that has several SCADApacks at remote sites and I need to make changes in their cellular network system. I have the .pia...
Replies
3
Views
1,887
Back
Top Bottom