PowerFlex 525 over Ethernet: running signal?.
Elcan
Apr 2008
NC
935
Hi all,
I'm programming a PowerFlex 525 over Ethernet for the first time, but I don't have the drive with me.
I need to identify which signal is the equivalent to "running".
My first guess is "Active". In the tag window it looks like VFD_1:I.Active.
My second guess is one of the bits under: VFD_1:I.DriveStatus.
I will appreciate your guidance and if you can point to a specific manual as a reference. I looked at a few and it is not clear for me which signal to use for this purpose.
I believe Active is what you are looking for. When we program these drives and want to Run the drive we give it the start cmd until we see that it is active. Same goes for stop we give the stop cmd until we see that it is no longer active.
Yes, Active means running in this case, meaning that the drive has been told to run. But to be clear, if you have given the drive a speed command of Zero, this bit will still show Active even though the motor is not actually turning. I generally use Active in conjunction with something more specific to the thing I want to be sure of, i.e. the speed is greater than zero, which you would get from the Drive Operational values
You can monitor the commanded frequency and other values by Going to the 525 module properties selecting change located under module definition and adding commanded frequency to the input data
In addition to .Active, you can use .AtReference
There are also .Accelerating and .Decelerating flags you can use. .AtReference means the drive has reached the commanded frequency.
Hi guys! We have a big project at work where we are migrating from 1305, 1336, 160, 70, and 40 drives to identical PowerFlex 525 models. Most...
886
Hi All, I am working on testing a project with a Powerflex 525, final project will be a 755, and I am trying to reset the Elapsed kWh meter over...
593
I am looking for some help with a project that I am working on to finish my maintenance apprenticeship. Any help would be greatly appreciated. My...
3,275
Good Morning , I have a quick question about the Powerflex 525 embedded ethernet drive. I'm using a CompactLogix 1769-L18 and using Ethernet...
1,762
Good Day Guys, I currently have a set up with 4 pieces of a 22-comm-e with 20 powerflex 4. I would like to move away from the daisy chain...
2,460