RSLogix 5000 PID Hydraulic Servo Valves for Position
timryder
Feb 2007
Macomb MI
176
Hey Guys,
Got an application where the Engineer purchased some Hydraulic Servo Valves and would like me to write a PID to control the position of the axis the Hydraulics are moving. There is an Absolute rotary encoder hooked up to this rotational axis and the general idea is he'd like to input a position in engineering units and have this things aggressively move towards that position until it gets very close in which it should slow down and stop.
So what's the best way to accomplish this? PID? I've never used it before so some serious help would be needed. The Valve is setup as analog output 8 bit and I have the Encoder as a 0-10v input. They're all working and talking over EtherNet/IP to my CompactLogix PLC.
As usual all help is appreciated.
I don't think the PID would work, IF I understand the application. The PID will never close the valve (unless you have a large overshoot) which will cause the hydraulics to continue to move. Example: If I'm controlling a steam valve to control temp, when my temp is at SP the valve wouldn't close. It would stay open to continue maintaining the temp.
I would write something that compared the SP to the feedback position and then adjust the output based on how far apart they are.
If you had a Control Logix and SSI feedback I would say get a 1756-M02AS card.
This could be a complicated application depending on several factors.
I am confused by your statement about the encoder. You say the axis is rotational? What happens when the encoder makes a full revolution?
8 bit DtoA will only work for crude positioning.
PLC scan times are not fast. Neither are the PLC AtoD cards.
What model valve are you using?
What is the mass?
What is the time of motion and how far?
What is the accuracy?
Chances are a Compact Logix will not do the job.
I would replace the analog encoder with an SSI encoder with as many bits of resolution you can afford. 16 bits is usually enough and not too expensive. If the rotational axis must make multiple turns then a multi turn SSI encoder is required. I would then get a RMC75E-MA1 from Delta Computer Systems.
If the system is designed right the tuning and motion control can be done in minutes.
Hi, Long time not in the forum, and not in the programming. I´m getting back. I was issued a conversion from RSLogix 500 to RSLogix 5000 (studio...
1,289
So I have a PID loop on an 1756-L61 running V17 software just for background. Also the PID PV is a pressure transmitter and the CV is speed sent...
894
Hi All, I have a PID control application that I would like to get your opinions on. As I am reality new to PID loops I am struggling somewhat...
4,283
Hi, I am confuse with the scaling tab on the PID dialog box. On the Process variable I am using a tag that is already scale. 0 to 16 Feet Level...
2,420
Hi I am trying to understand the best method of providing bumpless transfer to the PID function (not PIDE) The existing code shows In Manual...
4,616