BryanG
Member
Have a project where an incremental encoder (push/pull 24V d.c. output) will be 300 metres away from a Siemens S7-226 PLC. I am worrying that I will loose the signal in the cable, am I worrying about nothing? Have done some calculations and I reckon that at 55mA I would only loose 1 Volt, but long cable runs and noise always worry me. Frequency will be 200Hz maximum. My other option is to choose an encoder with a differential output and then before the PLC, invert one of the signals and combine them so that any noise cancels out, but I haven't been able to find a simple device to do this (probably me being thick). Either way I would obviously use screened cable, and with twisted pairs for the differential system.
I could get an encoder with a fibre output but the cable has to reeled in and out a lot so breakage would worry me. One end of the system is underground so wireless is out.
What's your thoughts?
Bryan
I could get an encoder with a fibre output but the cable has to reeled in and out a lot so breakage would worry me. One end of the system is underground so wireless is out.
What's your thoughts?
Bryan