WinCC Flexible RT 2008 connection problem

Hi,

I have a WinCC Flexible 2008 project. It is configured as a PC RT. If I use the Runtime on my laptop (development environment) it works fine; communicates to PLC, displays values etc as you would expect.

However, I have installed WinCC Flexible 2008 RT including the licences onto another PC and the project starts but there are just ## where all the values should be, and I don't see the pop-up window which says whether the connection was successful or not.

I can ping the PLC from the PC so actual connectivity shouldn't be an issue.

The PLCs are all on the schema 10.96.25.xxx whereas all the PCs (including my laptop) are on 10.96.17.yyy. If the problem was the different IP schema then why does my laptop work ok?

I have ethernet enabled as channel 2 and I can send the project from my laptop to the target PC with no problem, but for some reason the thing doesn't want to communicate with the PLC?

Is this a Netpro thing? I don't know much about Netpro! :-( In Netpro there is no line from the WinCC to the CPU.

CPU is a 317-2 dp/pn.

Thanks,

Martin
  Reply With Quote
Old March 28th, 2011, 01:24 PM   #2
userxyz
Member
United States

userxyz is offline
 
Join Date: May 2002
Location: any
Posts: 2,768
Pg/pc

Check PG/PC interface. Set it on TCP/IP.

Too see if there is a connection, place an alarm window and set System Alarms on. Then you can see what happens.

Quote:
Originally Posted by MartinW View Post
Hi,

I have a WinCC Flexible 2008 project. It is configured as a PC RT. If I use the Runtime on my laptop (development environment) it works fine; communicates to PLC, displays values etc as you would expect.

However, I have installed WinCC Flexible 2008 RT including the licences onto another PC and the project starts but there are just ## where all the values should be, and I don't see the pop-up window which says whether the connection was successful or not.

I can ping the PLC from the PC so actual connectivity shouldn't be an issue.

The PLCs are all on the schema 10.96.25.xxx whereas all the PCs (including my laptop) are on 10.96.17.yyy. If the problem was the different IP schema then why does my laptop work ok?

I have ethernet enabled as channel 2 and I can send the project from my laptop to the target PC with no problem, but for some reason the thing doesn't want to communicate with the PLC?

Is this a Netpro thing? I don't know much about Netpro! :-( In Netpro there is no line from the WinCC to the CPU.

CPU is a 317-2 dp/pn.

Thanks,

Martin

Last edited by userxyz; March 28th, 2011 at 01:26 PM.
  Reply With Quote
Old March 28th, 2011, 01:26 PM   #3
MartinW
Member
United Kingdom

MartinW is offline
 
Join Date: Apr 2008
Location: UK
Posts: 70
Hi,

Thanks for your quick reply. However on the target PC all that is installed in WinCC Flex runtime - so no PG/PC interface to use?

Thanks,

Martin
  Reply With Quote
Old March 28th, 2011, 01:29 PM   #4
userxyz
Member
United States

userxyz is offline
 
Join Date: May 2002
Location: any
Posts: 2,768
Pg/pc

When installing WinCC Flexible, PG/PC interface is installed as well. Go to configuration panel and set the interface right so that Flexible know wich protocol it must use.


Quote:
Originally Posted by MartinW View Post
Hi,

Thanks for your quick reply. However on the target PC all that is installed in WinCC Flex runtime - so no PG/PC interface to use?

Thanks,

Martin
  Reply With Quote
Old March 28th, 2011, 01:34 PM   #5
MartinW
Member
United Kingdom

MartinW is offline
 
Join Date: Apr 2008
Location: UK
Posts: 70
ok, I was a dumba$$, I finally found PG/PC interface in control panel!

doh!
  Reply With Quote
Old March 28th, 2011, 01:42 PM   #6
userxyz
Member
United States

userxyz is offline
 
Join Date: May 2002
Location: any
Posts: 2,768
np

np

Quote:
Originally Posted by MartinW View Post
ok, I was a dumba$$, I finally found PG/PC interface in control panel!

doh!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
IO field reading problem (WinCC Flexible) vojvoda1982 LIVE PLC Questions And Answers 4 November 21st, 2010 08:30 AM
Siemens TP270-10" Screen Download problem with WinCC 2008 o4a0e1 LIVE PLC Questions And Answers 5 October 10th, 2009 02:23 AM
Drawings in WinCC flexible 2008 thorgalrose LIVE PLC Questions And Answers 6 August 4th, 2009 04:52 AM
Wincc Flexible Runtime / Archives for RT dwcy LIVE PLC Questions And Answers 9 March 18th, 2008 02:24 PM
WinCC Flexible - appearence problem vlad.colesnic LIVE PLC Questions And Answers 3 July 27th, 2007 02:24 AM


All times are GMT -4. The time now is 03:16 PM.


.