hello,
i am using compact logix L16ER PLC and emerson Micro motion 5700 MFM.
i used TOTALIZER block in studio 5000 to calculate transferred quantity.
i am facing issue to calculate accurate transfered quantity.
MFM gives flow rate of air....so how can i calculate actual product flow rate so that i get exact quantity.
MFM gives data of flow rate,density,gain and temperature...how to use this all parameters to knw actual flow rate of product.
thanks in advance
i used TOTALIZER block in studio 5000 to calculate transferred quantity....
The OP is not clear.
Do we want to know the instantaneous flow rate at any single point in time, e.g. SCFM (standard cubic feet per minute), or the accumulated transferred quantity between two times (or between two events) e.g. m**3 (cubic meters)?
What is your skill level? Engineer? Technician?
Note that the 5700 appears to be able to report both instantaneous flow rate and accumulated transferred quantity directly. For the latter the PLC would need to be able to reset the 5700 totalizer at the time of a start event.
please find attached images
MFM DETAILS LINK https://******/3gh3HjI
even if there is no oil passing through mass flow meter still it gives flow rate due to air.
so thats the reason, i dont get exact quantity of transferred material....
can we detect air/gas in oil????
If that is the case then the flow meter is not installed properly, the flow meter should be installed so that it is always full. In other words any shut off valves are normally installed upstream of the flow or flow meter fitted in a well of the pipe to keep it full, some will also give a signal if random readings indicating there is cavity in the tube (empty pipe detection). The other thing you could do is if the flow is controlled via a pump or valve , when the pump stops/ valve closes (give a little delay to allow the flow to stop) and disable the totalizer, this will reduce the error considerably.
I want to connect my allen bradly micro logic 1400 to and emerson epp servo drive via the ethernet IP connection, has anyone done this? if so are...
3,898
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
94
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
100
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
969
Hello all, First time poster, long time viewer of these forums. Could not find my solution on here. We have had issues with a Comm Fail on an...
378