Scaling analog inputs for 1769-IF8 card in CompactLogix
MartyMaucher
May 2014
Pensacola
91
I know this has been covered before, but I can't get this scaling to work in Logix Designer/CompactLogix 1769-L33ER project. I tried to:
- Configure the range in the analog input card properties: Not in CompactLogix
- Use Scaled Parameter (SCP) instruction - does not exist
- Use a custom AOI instruction from the AB SCP.L5X file: File does not open - error on line 1 as shown below
Is there a latest and greatest way to scale these inputs?
You could roll your own using the CPT function, or use function block SCL.
Just to check, you are trying to import the aoi by right clicking on Add-On Instructions and doing an import right?
Oops... I was trying to open the file as a project. Thanks for that - I now have the imported SCP function. Any idea what the Input_Min and Max are?
Table 3.17 Valid Input Data from this document should answer that!
1769-um002_-en-p.pdf
depends a bit on the input voltage/current selection
By far the easiest method is to use an AOI to create the SCP function for you. Rockwell has created one and posted it on their website, or you can use the one i have attached.
hi i am pretty good at programming ab plc . i have never had any experience with analog controls . i currently need to set up a slc 5/02...
26,120
I am familiar with RSLogix 500 and I have done multiple applications using analog. I have to do a project using Direct Soft 32. I am going to use...
15,346
Hello, We monitor the temperature of a pipe via a 4-20mA temperature transducer. This goes into DB135(Read Analog Inputs). The issue I have is the...
628
Hi all! I have a question about RSLOGIX and Analog input/output scaling So we have an existing controller with an IF8I and OF81 card. My...
936
I’m trying to perfect the HMI interface for analog configuration. I’ve provided the user the same options for all analog inputs, as follows...
1,675