Nema 7 Classification Help

I have a control station that just has two selector switches on it in a Class 1 Div 2 Area. I'm providing for this control station a Stainless Steel Nema 4X enclosure and a Cutler and Hammer Selector switch that is rated for Class 1 Div 2 area. The Selector switch contacts are Hermetically Sealed.

My specification is calling for a Nema 4x and Nema 7 enclosure. Do I have a case to state that a Nema 4X enclosure with the hemertically sealed contacts does not need a Nema 7 enclosure rating?

RRoc

Last edited by RRoc; January 28th, 2017 at 01:50 PM.
  Reply With Quote
Old January 28th, 2017, 02:18 PM   #2
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,492
Yes you have a case. The risk is, some day someone may replace one of those contact blocks with the non-hermetically sealed versions, whereas with a NEMA 7 enclosure, that would not matter. So it depends a lot on the professional integrity of the user; i.e. do they take things like this seriously, or are they populated by grunts who just "get 'er done". If it's someplace like a refinery, they generally know the score but if it's a Cl1 Div 2 environment in a gas station, I would not trust it.
  Reply With Quote
Old January 28th, 2017, 02:31 PM   #3
jkerekes
Member
United States

jkerekes is online now
 
jkerekes's Avatar
 
Join Date: Aug 2007
Location: NJ
Posts: 2,155
I'm not sure about the hermetically sealed contacts also. You have no way to know if somehow the sealing fails.
__________________
John
  Reply With Quote
Old January 28th, 2017, 03:12 PM   #4
diat150
Lifetime Supporting Member
United States

diat150 is offline
 
Join Date: Mar 2006
Location: Louisiana
Posts: 1,235
Quote:
Originally Posted by jkerekes View Post
I'm not sure about the hermetically sealed contacts also. You have no way to know if somehow the sealing fails.

Im not a true expert on this, but I dont think that is how it works. If it is a class 1 div 2 area you use class 1 div 2 components. You dont worry about if something fails.
  Reply With Quote
Old January 28th, 2017, 07:22 PM   #5
jkerekes
Member
United States

jkerekes is online now
 
jkerekes's Avatar
 
Join Date: Aug 2007
Location: NJ
Posts: 2,155
I think your correct technically. They are allowed. But they are still impossible to verify.
__________________
John
  Reply With Quote
Old January 28th, 2017, 09:30 PM   #6
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,163
Since you have only 2 switches,

you may want to consider buying an ab 800h box and 2 of their switches
its a nema 7 enclosure and so are the switches. Use rigid conduit all the way back to the non hazardous area and use seal offs. I don't think barriers will be required.

this is what we did in a class 1 div 1 environment.

regards,
james
  Reply With Quote
Old January 29th, 2017, 10:57 AM   #7
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,492
Assuming from the description that you are using contact elements that are UL listed as Class 1 Division 2, as are offered by most of the major mfrs, the concept of using them in a standard NEMA 4 enclosure as opposed to a NEMA 7 enclosure when they are the ONLY elements in the box, such as a control station like yours, is the EXACT intended use that they are listed for. Failure risk is already part of the process of being listed by UL.

My point was the future risk based on the kind of end user environment: conscientious industrial facility with rules and training, or casual user who may bring in untrained unqualified people to fix things who do not understand the risks of using the wrong components. If you use the NEMA 7 route, standard pilot devices can't be mounted in them but the rating of the contact blocks inside becomes irrelevant. It essentially forces them to use the right parts. If it's a refinery or processing facility however, that's typically not much of a risk.
  Reply With Quote
Old January 29th, 2017, 04:44 PM   #8
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,163
One thing you MUST remember.
NEC70 rules state that no device can be use in an environment unless it is listed for that use.
When in a classified area, you must adhere to the hazardous section of the code - the 500's

you must also look at the rules regarding purging / pressurizing enclosures since it is a nema 4 enclosure.

While using sealed contacts may be allowed(i'm not convinced you can), you still have to have safety barriers and seal offs to prevent wiring shorts, replacing the contacts with non sealed ones, and open space back to the control panel and creating a hazard.

james
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Nema 1 = IEC? NetNathan LIVE PLC Questions And Answers 2 August 4th, 2016 11:46 AM
NEMA 12 Enclosure damiens LIVE PLC Questions And Answers 5 July 26th, 2016 03:26 PM
Nema 4x VFD RSL LIVE PLC Questions And Answers 21 November 5th, 2014 05:24 PM
iPad Nema rating curlyandshemp LIVE PLC Questions And Answers 8 January 5th, 2012 10:30 PM
NEMA 34 stepper gearbox rpoet LIVE PLC Questions And Answers 6 October 22nd, 2009 10:21 AM


All times are GMT -5. The time now is 11:58 AM.


.