Nema 7 Classification Help
RRoc
Jan 2017
California
45
I have a control station that just has two selector switches on it in a Class 1 Div 2 Area. I'm providing for this control station a Stainless Steel Nema 4X enclosure and a Cutler and Hammer Selector switch that is rated for Class 1 Div 2 area. The Selector switch contacts are Hermetically Sealed.
My specification is calling for a Nema 4x and Nema 7 enclosure. Do I have a case to state that a Nema 4X enclosure with the hemertically sealed contacts does not need a Nema 7 enclosure rating?
RRoc
Yes you have a case. The risk is, some day someone may replace one of those contact blocks with the non-hermetically sealed versions, whereas with a NEMA 7 enclosure, that would not matter. So it depends a lot on the professional integrity of the user; i.e. do they take things like this seriously, or are they populated by grunts who just "get 'er done". If it's someplace like a refinery, they generally know the score but if it's a Cl1 Div 2 environment in a gas station, I would not trust it.
I'm not sure about the hermetically sealed contacts also. You have no way to know if somehow the sealing fails.
Im not a true expert on this, but I dont think that is how it works. If it is a class 1 div 2 area you use class 1 div 2 components. You dont worry about if something fails.
I think your correct technically. They are allowed. But they are still impossible to verify.
Since you have only 2 switches,
you may want to consider buying an ab 800h box and 2 of their switches
its a nema 7 enclosure and so are the switches. Use rigid conduit all the way back to the non hazardous area and use seal offs. I don't think barriers will be required.
this is what we did in a class 1 div 1 environment.
regards,
james
Assuming from the description that you are using contact elements that are UL listed as Class 1 Division 2, as are offered by most of the major mfrs, the concept of using them in a standard NEMA 4 enclosure as opposed to a NEMA 7 enclosure when they are the ONLY elements in the box, such as a control station like yours, is the EXACT intended use that they are listed for. Failure risk is already part of the process of being listed by UL.
My point was the future risk based on the kind of end user environment: conscientious industrial facility with rules and training, or casual user who may bring in untrained unqualified people to fix things who do not understand the risks of using the wrong components. If you use the NEMA 7 route, standard pilot devices can't be mounted in them but the rating of the contact blocks inside becomes irrelevant. It essentially forces them to use the right parts. If it's a refinery or processing facility however, that's typically not much of a risk.
One thing you MUST remember.
NEC70 rules state that no device can be use in an environment unless it is listed for that use.
When in a classified area, you must adhere to the hazardous section of the code - the 500's
you must also look at the rules regarding purging / pressurizing enclosures since it is a nema 4 enclosure.
While using sealed contacts may be allowed(i'm not convinced you can), you still have to have safety barriers and seal offs to prevent wiring shorts, replacing the contacts with non sealed ones, and open space back to the control panel and creating a hazard.
james
I have noticed that many HMI have a Nema rating of Mena 4/4X (indoor use only) Does anyone have any guesses as to what the constraints are that...
1,800
Looking for some explanation/history between North American electrical symbols standards (how they relate, what are the latest, what is the...
1,707
Good evening gentlemen, I am looking for VFD with NEMA 4x rating. It's a small one, single phase 208/230 input, 208 three phase motor 8.46 Amps...
3,485
Hello, are there any standards for control wires naming rules? I have to set them up in my project (see pic). What is usually prefix and...
2,236
Looking for a brief explanation for the NEMA MG-1 Part 31 standard for the actual voltage values. In reading many articles I have seen 1488Vp...
1,404