Help!!! Modbus/hart troubleshooting

Hello,

My goal is to have a micrologix 1400 plc read data from a hart modem HRT-710. so I can read flow and totalizer and display them on HMI.

We have 3 other sites that are identical to this new site. I used all same programming for the PLC, flow meter (flowmag50W) and Hart modem (HRT-710).

the only difference is the new site has only one flow meter instead of 2 flowmeters, for that reason, I made sure to select point to point inside the hart modem (HRT -710).

I proved that the HART 710 modem is not defective by swapping with a unit from a different site.

I can read flow data and totalizer data from the flow meter via hart using the HRT-710 modem software, and using PC based software(Modbus master tool) but this was accomplished by using the RS 323 on the HRT 710. note that the HRT 710 has RS 232 and RS 485 to communicate, but only one can be used at the time.

When the PLC tries to retrieve data from the HRT 710 using a message instruction, it doesn't work. Message keeps saying error 37 " time out in local processor. this PLC programming is the same as other sites.

On the Modbus side, I also have one VFD that is communicating perfectly to the PLC, But not the hart modem?... I'm using 400 ohms resister for termination on both sides, I tried 250 ohms but didn't make a difference.

Also, the baud rate is same on all slaves and master.
And HART modem hart 710 is using net ID 3, PLC message instruction to pool the modem is using that same net ID 3.
and cable runs are very short.

I'm very confused, If any one has a suggestion. please let me know...!!
Thank you very much
  Reply With Quote
Old December 5th, 2017, 08:40 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,112
Interesting challenge !

My reading of your post is that you're using the Channel 0 port on the MicroLogix 1400 in Modbus RTU master mode, with the channel set for "485 - No Handshaking", to send Modbus RTU messages to both an AC drive and the HART modem.

Describe your actual RS-485 wiring from the MicroLogix to the AC drive and the HART modem.

Are you using two conductors, or three ? How are the signal common or comms grounds connected together ?

Have you tried to disconnect the AC drive and poll the HART modem only ?

This is a bit of a detour, but I'm curious about what you're doing with the drive and the MicroLogix. Are your start/stop/reference commands going over Modbus, or are you reading diagnostic data out of the drive ?
  Reply With Quote
Old December 5th, 2017, 10:43 PM   #3
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,802
There is no commonality between the HART protocol and the Modbus protocol, other than they can potentially use a common hardware bus at the master end.

The HART modem strips HART data off the field device, but that data is packed in HART comm packets, whatever those are and they're not Modbus packets.

HART enabled I/O is typically high end AI or AO cards for ControlLogix level controllers.

I think Moore might have a HART/Modbus gateway, and if it were a HART madter/Modbus server/slave then your 1400 would need to be a Modbus client/master.
  Reply With Quote
Old December 5th, 2017, 11:33 PM   #4
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,119
danw, I think the OP has this..

http://www.icpdas.com/root/product/s...y/hrt-710.html
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old December 6th, 2017, 01:10 AM   #5
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,802
Thanks, Mickey, for the heads-up. It's a Modbus/HART Gateway, not a HART modem.

1.
Quote:
Originally Posted by richleva View Post
the only difference is the new site has only one flow meter instead of 2 flowmeters, for that reason, I made sure to select point to point inside the hart modem (HRT -710).
Most HART devices come with a factory default HART address zero for point-to-point HART comm, typically with a handheld communicator or a HART modem and software, like Pactware.

I would think that point-to-point mode on the HART side of the Gateway would mean the Gateway expects to talk to a single HART slave device at address zero. Addresses above zero are for multidrop or mux'd modes.

Is the field device at HART address zero?

2. Termination resistance for a point-to-piint or multidrop RS-485 network is typically 120 ohms, and only at ends of the network, typically master at one end and the last multidrop slave on the other end.

A HART modem needs a minimum of 230 ohms resistance in series in the analog 4-20mA loop to be able to develop sufficient signal amplitude to 'read' by the receiver. That resistance could conceivably be part of the HART side of the Gateway, maybe switchable in or out of the circuit, depending on how it's designed.
  Reply With Quote
Old December 6th, 2017, 01:32 AM   #6
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,802
1. Does the Parity setting on RS-485 side of Gateway match the PLC and drive parity settings?

2. Have you tried swapping the RS-485 A/B or (+)/(-) lines at the 485 side of hhe Gateway?

3. Is the any hardware or firmware 'switch' that flips betwen RS-232 and RS-485 on the Gateway?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Profibus Troubleshooting - LinkedIn group danw LIVE PLC Questions And Answers 0 April 8th, 2013 11:51 AM
Troubleshooting Remote Slave D4-RS Link light error wildcatherder LIVE PLC Questions And Answers 1 September 14th, 2009 12:15 PM
Servo Troubleshooting - the endless loop TimothyMoulder LIVE PLC Questions And Answers 6 June 8th, 2006 01:20 PM
VFD Troubleshooting GregPLC LIVE PLC Questions And Answers 11 April 24th, 2005 01:55 PM
TROUBLESHOOTING METHODS? Interview question rook LIVE PLC Questions And Answers 25 February 12th, 2004 12:09 PM


All times are GMT -5. The time now is 01:32 AM.


.