Flowmeter 4-20mA Input Signal
I have a 4-20mA Electromagnetic Flow meter which is externally powered. I have a 24VDC supply powering the meter (which is powering up correctly - screen lights up and shows values etc.)
I am using a Siemens SM-1234 4AI card. Separate from the power, I have my "0+" on the AI module hooked up to "I+" on the flowmeter and the "0-" on the AI Module hooked up to "COM" on the flowmeter. When I power up the rack - the red fault light comes on the card and the processor.
Any idea what I am doing incorrectly? Thanks!
Old February 6th, 2018, 12:45 PM   #2
Dood
United States
Dood is offline
To clarify - the Diagnostics show "High Limit Exceeded" which would make me think short circuit, but I don't see how that's possible.
Thanks!
Old February 6th, 2018, 01:07 PM   #3
cardosocea
United Kingdom
cardosocea is offline
Who is supposed to be powering the loop? The IO card or the Flowmeter?
If they are both trying to power the loop, what you mentioned can happen.
Old February 6th, 2018, 02:11 PM   #4
Dood
United States
Dood is offline
The flowmeter should be powering the loop. The IO card cannot.
I've attached the wiring diagram that I've found for the flowmeter - it was ordered from China so the language is a little confusing and the terminals aren't consistent. I'm currently trying to use the 4-wire configuration with no luck.
Thanks again!
Old February 6th, 2018, 03:16 PM   #5
cardosocea
United Kingdom
Also, is the card configured for current measurement?
Do you have a loop calibrator to figure out one of these at a time?
Old February 6th, 2018, 03:33 PM   #6
Dood
United States
Dood is offline
The card is configured for 0-20mA input.
I have a fluke 787 and when I use the Source mA function I put my "+" to the "0+" terminal and the "-" to the "0-" terminal, the module flashes the same error light. Like it won't even accept a simulated 4-20mA from my Fluke. Am I doing something wrong with the fluke?
Old February 6th, 2018, 03:58 PM   #7
tarik1978
Morocco
tarik1978 is offline
Is the card correctly configured did try another channel?
As a test, reconfigure the hardware to 0-10 or +/- 10V rather than 4-20mA.
Now across the input terminals for that channel, add in a 500 Ohm resistor.
Now measure the channel signal in voltage right across those terminals.
If it reads properly and stays in range while you operate the field device, your field device is working properly.
If you find the voltage runs high and out of range, your field device may not be configured properly, or the wiring may have been done incorrectly.
Old February 6th, 2018, 04:02 PM   #8
tarik1978
Morocco
If the flowmeter is 4_20mA then the card should be configured the same
Old February 6th, 2018, 04:12 PM   #9
Dirt
Sweden
Dirt is offline
Did you try to bridge M to 0-?
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Time between output signal and input signal mangan LIVE PLC Questions And Answers 5 July 7th, 2016 03:02 AM
Direct PLC Dl05 controller with a 30 gpm flowmeter input kickford1 LIVE PLC Questions And Answers 21 March 4th, 2014 11:48 AM
Servo Motion Based On PLC analog input signal kthompson613 LIVE PLC Questions And Answers 0 December 16th, 2013 12:14 PM
Scalling for analog input module - SLC 5/04 ckchew666 LIVE PLC Questions And Answers 1 May 15th, 2008 10:31 AM
PID Loop Update time and external trigger leitmotif LIVE PLC Questions And Answers 50 May 9th, 2005 06:46 PM