Flowmeter 4-20mA Input Signal

Hi,

I have a 4-20mA Electromagnetic Flow meter which is externally powered. I have a 24VDC supply powering the meter (which is powering up correctly - screen lights up and shows values etc.)

I am using a Siemens SM-1234 4AI card. Separate from the power, I have my "0+" on the AI module hooked up to "I+" on the flowmeter and the "0-" on the AI Module hooked up to "COM" on the flowmeter. When I power up the rack - the red fault light comes on the card and the processor.

Any idea what I am doing incorrectly? Thanks!
  Reply With Quote
Old February 6th, 2018, 12:45 PM   #2
Dood
Member
United States

Dood is offline
 
Join Date: Feb 2018
Location: New Orleans
Posts: 9
To clarify - the Diagnostics show "High Limit Exceeded" which would make me think short circuit, but I don't see how that's possible.

Thanks!
  Reply With Quote
Old February 6th, 2018, 01:07 PM   #3
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 744
Who is supposed to be powering the loop? The IO card or the Flowmeter?

If they are both trying to power the loop, what you mentioned can happen.
  Reply With Quote
Old February 6th, 2018, 02:11 PM   #4
Dood
Member
United States

Dood is offline
 
Join Date: Feb 2018
Location: New Orleans
Posts: 9
Quote:
Originally Posted by cardosocea View Post
Who is supposed to be powering the loop? The IO card or the Flowmeter?

If they are both trying to power the loop, what you mentioned can happen.

The flowmeter should be powering the loop. The IO card cannot.

I've attached the wiring diagram that I've found for the flowmeter - it was ordered from China so the language is a little confusing and the terminals aren't consistent. I'm currently trying to use the 4-wire configuration with no luck.

Thanks again!
Attached Images
File Type: jpg Wiring.jpg (20.9 KB, 46 views)
  Reply With Quote
Old February 6th, 2018, 03:16 PM   #5
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 744
Also, is the card configured for current measurement?

Do you have a loop calibrator to figure out one of these at a time?
  Reply With Quote
Old February 6th, 2018, 03:33 PM   #6
Dood
Member
United States

Dood is offline
 
Join Date: Feb 2018
Location: New Orleans
Posts: 9
Quote:
Originally Posted by cardosocea View Post
Also, is the card configured for current measurement?

Do you have a loop calibrator to figure out one of these at a time?
The card is configured for 0-20mA input.

I have a fluke 787 and when I use the Source mA function I put my "+" to the "0+" terminal and the "-" to the "0-" terminal, the module flashes the same error light. Like it won't even accept a simulated 4-20mA from my Fluke. Am I doing something wrong with the fluke?
  Reply With Quote
Old February 6th, 2018, 03:58 PM   #7
tarik1978
Member
Morocco

tarik1978 is offline
 
Join Date: Mar 2010
Location: casablanca
Posts: 287
Is the card correctly configured did try another channel?
As a test, reconfigure the hardware to 0-10 or +/- 10V rather than 4-20mA.

Now across the input terminals for that channel, add in a 500 Ohm resistor.

Now measure the channel signal in voltage right across those terminals.

If it reads properly and stays in range while you operate the field device, your field device is working properly.

If you find the voltage runs high and out of range, your field device may not be configured properly, or the wiring may have been done incorrectly.
  Reply With Quote
Old February 6th, 2018, 04:02 PM   #8
tarik1978
Member
Morocco

tarik1978 is offline
 
Join Date: Mar 2010
Location: casablanca
Posts: 287
If the flowmeter is 4_20mA then the card should be configured the same
  Reply With Quote
Old February 6th, 2018, 04:12 PM   #9
Dirt
Member
Sweden

Dirt is offline
 
Join Date: Apr 2008
Location: Stockholm
Posts: 153
Quote:
Originally Posted by Dood View Post
The card is configured for 0-20mA input.

I have a fluke 787 and when I use the Source mA function I put my "+" to the "0+" terminal and the "-" to the "0-" terminal, the module flashes the same error light. Like it won't even accept a simulated 4-20mA from my Fluke. Am I doing something wrong with the fluke?
Did you try to bridge M to 0-?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Time between output signal and input signal mangan LIVE PLC Questions And Answers 5 July 7th, 2016 02:02 AM
Direct PLC Dl05 controller with a 30 gpm flowmeter input kickford1 LIVE PLC Questions And Answers 21 March 4th, 2014 11:48 AM