Customer got hit with the Nor'Easter and just got power back this AM.
Trying to solve a problem where they have (4) 1771-IFE (series C) modules that are all flashing green. I understand this means no configuration loaded, but with the PLC in run mode and the block transfers executing, how is there no configuration loaded?
Trying to save myself a road trip today, although it doesn't seem likely. Unfortunately, AT&T is having issues, so their VPN is down.
There are other analogs on Flex I/O that are reading fine, so obviously the program is still active. Not sure why these four modules are not cooperating.
Old March 4th, 2018, 11:23 AM   #2
Mickey
United States
Mickey is offline
Mickey's Avatar
Have you tried to go to program mode and back to run mode? (with key switch)
The block transfer read may be flashing but the block transfer write may only execute once ( depending on how its programed). Manually forcing it thru software?
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old March 4th, 2018, 11:31 AM   #3
phuz
United States
phuz is offline
You're probably right. These particular BTWs have a power-up bit (XIC) that energizes the BTW, but if the module is not configured, it should be triggering the BTW. I'm guessing this is the hangup, although without the VPN right now, I can't see. I'm trying to get the customer to get online with it first.
However, one of those four modules has a S:1/15 bit to trigger it, so I would expect that one to work, at least.
Old March 4th, 2018, 12:12 PM   #4
Ron Beaufort
United States
Ron Beaufort is offline
Ron Beaufort's Avatar
are the IFE modules all located in the "Local" chassis - (with the processor) or are they located in a "Remote" chassis? ...
and just to make sure - please confirm that the processor is actually a PLC-5 (specifically, it's NOT a Control/CompactLogix running the older 1771 hardware) ...
__________________
2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
I once was lost, but now am found, was blind, but now I see.
Old March 4th, 2018, 03:20 PM   #5
phuz
United States
phuz is offline
Haha, yes it's a PLC-5. All local I/O.
I cycled power, pulled all modules except the IFE, still had flashing light. Killed power, pulled the battery for a minute, re-downloaded the program and BINGO...it was back. Somehow something was corrupted and reset during a fresh download. We are upgrading this PLC-5 in the next few months.
Old March 4th, 2018, 03:22 PM   #6
Mickey
United States
Mickey is offline
Mickey's Avatar
Memory module??
__________________
Mickey
Old March 4th, 2018, 03:23 PM   #7
phuz
United States
phuz is offline
Memory module??
It does have one, yes.
Old March 4th, 2018, 03:25 PM   #8
Mickey
United States
Mickey is offline
Mickey's Avatar
Store the latest program, just to be sure.
__________________
Mickey
Old March 4th, 2018, 03:26 PM   #9
phuz
United States
phuz is offline
Yup, did that before I left.
Old March 5th, 2018, 11:04 AM   #10
TheWaterboy
United States
TheWaterboy is offline
TheWaterboy's Avatar
and make sure the backplane switch is set to load it on corrupted memory... Just saying...
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
PLC loose program after power outage or if PLC gets turned off koliza1 LIVE PLC Questions And Answers 5 August 3rd, 2016 03:08 PM
2 24VDC power supplies cskaggs2 LIVE PLC Questions And Answers 5 September 15th, 2010 11:24 PM
1771 ife input caculation helloooo LIVE PLC Questions And Answers 2 November 21st, 2006 06:26 PM
1771 ife configuration helloooo LIVE PLC Questions And Answers 1 November 21st, 2006 03:17 PM
Loop Powered Instruments sparky64 LIVE PLC Questions And Answers 7 October 4th, 2006 01:41 AM