I understand that all physical inputs are scanned during the "input scan" before the "program scan" phase.
But is this true for internal relay, contacts & registers also?
i.e.(1) Are internal relays energised during "Output scan phase" or do they get energised immediately as the rung logic goes true?
2) The state of contacts corresponding to internal relays: Is it checked only at the beginning of the program or is it checked each time the element is encountered?
The "How a ladder is scanned" topic in your contents seems to suggest that internal contacts are checked each time they are encountered in a rung. Your help will be highly appreciated.
regards
Viswesh
I realize this can be tough to understand at first, so instead of thinking about the physical I/O as being "scanned", think of it as being "updated".
Without getting too confusing, the answers to your questions (based on how you seem to see it) would be...
1.)All coils (inputs, outputs, internal coils) are "energized" (or "de-energized") immediately as the rung logic goes true/false.
2.)The state of contacts are checked each time they are encountered.
At the end of the scan, the physical outputs are "updated" with the current state. Therefore, the outputs will reflect the last state they are in at the end of the scan. Then the PLC gets "updated" with the physical state of the inputs, and the state of the inputs will remain constant for the current scan.
Get it?...
beerchug
-Eric
Hi, I understand that all physical inputs are scanned during the "input scan" before the "program scan" phase. But is this true for internal...
18
27,257
The client has an application that when communication between the PLC and the Factory Talk VIEW supervisory fails, the object in the supervisory...
289
Hello everyone; I have Mitsubishi PLC FX3U 32M in hydropower plant governor, an error message popped up when a technician was working on an...
373
Kindly, we are having a problem on a machine during night shifts, while no engineering tool is online. So, we were thinking of programming some...
760
Hello. If anybody has seen this before and could provide some clues I and some other people would be extremely grateful if you can share such...
1,338