Power Flex, Drive Logix and Control Logix

I have 5 PowerFlex 700SE drives that are connected via Control Net.
These drives are also connected to each other with a Sync Link module. There is a Drive Logix 5720 attached to each drive. The CPU is a Control Logix 1756-L63.

I have been looking at the tags in each of the Drive Logix controllers to make sure I can tell where the tags come from or go to. I have come to a point to where I am truly stumped.


This is a tag that is in one of the Drive Logix controllers. I know that K_COMRST is an alias to Drive:I.UserDefinedIntegerData[0].0. After some investigating the only place I can figure out where this comes from is using PowerFlex 700S Operating Terminal software.



Shown above is what I get when I connect to this drive. Now you can see K_COMRST "Variable Name". What I do not understand is where this originated from or any of these "Variables"? The green symbols: ACONF,ASR,blklib,COM etc. when I look at their properties are called modules. Where did these come from? I got into this situation last week where our press would not run. Basically I had to right click on some of the modules;COM, JBAR and some others and force them in run mode. They had little red marks beside them which meant they where stopped for some reason. My biggest confusion is where do all of these variables come from? I can look at most of the tags on this monster press and figure out where they originate or go to. These drive tags have me confused.

I am assuming that Drive:I.UserDefinedIntegerData[0].0 is an input to the Drive Logix controller from the drive. I understand that this is a "USER" Defined Integer. What I cannot find is what kind of data did the user assign for this tag. Below is a pic of the module defined tags for this drive.


I tried using Drive Executive to see what might be going on, but only got more confused. Below is what found connecting to the drive.


If I am thinking right, then Paramater 658 holds that data being put into Drive:I.UserDefinedIntegerData[0]. What I do not understand is that Parameter 658 when I monitor it with Drive Executive has no value. It also is not linked to any other parameter.

I have looked through every Drive Logix and Power Flex manual and cannot seem to understand this. If anybody has the time to help me with my confusion I would appreciate it.
Thank You
Tim
  Reply With Quote
Old January 4th, 2007, 02:22 PM   #2
Tim
Member
United States

Tim is offline
 
Tim's Avatar
 
Join Date: May 2002
Location: Indiana
Posts: 291
Bump...
Just in case an AB guru missed this thread.
  Reply With Quote
Old January 4th, 2007, 06:37 PM   #3
MichaelG
Member
Australia

MichaelG is offline
 
Join Date: Nov 2006
Location: Brisbane
Posts: 685
Drive pointers

Possible pointer to your problem
The Power Flex uses links to map what you send via communications Parameter 658 has a "source parameter" where it gets its actual value from.
To view
Open the Drive in drive executive (online or a current offline file)
Navigate to parameter 658 in the "linear List" and look for the "Source Parameter"


Look up the source parameter for what the value means

Right Click on 658 for properties and link source for another method to find out where the value comes from.

Last edited by MichaelG; January 4th, 2007 at 06:41 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
control logix PIDE error vram LIVE PLC Questions And Answers 6 October 6th, 2006 02:47 AM
Producer Consumer Messging between Control Logix & Compact Logix plcnovel LIVE PLC Questions And Answers 15 July 24th, 2006 11:04 AM
Control logix to Power Flex 70 using ANACANDA kamalaitounejjar LIVE PLC Questions And Answers 5 May 16th, 2006 11:31 AM
Compact Logix to Power Flex 700 JChapman LIVE PLC Questions And Answers 2 March 28th, 2005 06:21 AM
Control Logix Power Points Steve Crotty LIVE PLC Questions And Answers 0 March 4th, 2005 11:17 AM


All times are GMT -5. The time now is 06:17 PM.


.