AB DH485, SLC 5/04, AIC+ Comm Failure

Hello all. I would appreciate your help in troubleshooting an AB multi-drop DH485 network.
Our company was retained to modify existing machinery. The network issue became apparent when we attempted to connect our PC into an existing PLC/HMI DH485
network by adding a 1761-NET-AIC Ser. B. One machine was successfully connected; two were not able to be connected or appear in RSLinx.

Machine 1 (worked):
SLC 5/04 1747-L541 Ser. B FRN 3 OS 401; Chan. 0 configured for DH485, 19200, Node 1. 1761-CBL-PM02 connecting from SLC to AIC+ Mini-DIN RS232 port
PV550 2711-B5A5 FRN 4.10; 19200, Node 2. Serial cable connecting from PV to AIC+ DE9 RS232 port
Laptop running RSLinx 2.57, using 1747-UIC; 1761-CBL-AS03 connecting from UIC to AIC+ RS485 port; AB_UIC driver, Node 0
AIC+ externally powered

PC was able to go online with SLC and download to PV.

Machine 2 (failed):
SLC 5/04 1747-L541 Ser. B FRN 3 OS 401; Chan. 0 configured for DH485, 19200, Node 1. 1761-CBL-PM02 connecting from SLC to AIC+ Mini-DIN RS232 port
PV550 2711-B5A5 FRN 2.00; 19200, Node 2. Serial cable connecting from PV to AIC+ DE9 RS232 port
Laptop running RSLinx 2.57, using 1747-UIC; 1761-CBL-AS03 connecting from UIC to AIC+ RS485 port; AB_UIC driver, Node 0
AIC+ externally powered

No nodes found active in RSLinx.

Machine 3 (failed):
SLC 5/04 1747-L541 Ser. B FRN 3 OS 401; Chan. 0 configured for DH485, 19200, Node 1. 1761-CBL-PM02 connecting from SLC to AIC+ Mini-DIN RS232 port
PV550 2711-B5A9 FRN 3.10; 19200, Node 2. Serial cable connecting from PV to AIC+ DE9 RS232 port
Laptop running RSLinx 2.57, using 1747-UIC; 1761-CBL-AS03 connecting from UIC to AIC+ RS485 port; AB_UIC driver, Node 0
AIC+ externally powered

No nodes found active in RSLinx.


Is the PV firmware version to blame here? Any thoughts or suggestions?

Best regards,
gnieport
  Reply With Quote
Old August 31st, 2011, 01:40 PM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,957
EDIT: I think I understand better after a re-read.

The PV firmware should not affect DH485 functionality as far as I know, but it certainly can affect the PB32 application. In PB32 you can choose the older firmware versions for most hardware, and then do a Save As .pva (or do a Application...Validate All...) to ensure that the application is compatible with the older firmware.

But if RSLinx can't see all the nodes once connected, then you haven't even got that far yet. You're using the latest version, so just a WAG, but maybe the eds files for the antique panelviews have been left out? Are you seeing yellow question marks or anything?

Also, another WAG, but we've had trouble with DH485 drivers "not liking it" when we moved a laptop from one machine to another...we ended up deleting the driver and creating it again in order to get the RSWho to "let go" of some nodes it was displaying incorrectly. Blowing away the harmony files is another suggestion that can't hurt.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.

"You can lead a horse to water but if he's got his head up his as$ he may die of thirst anyway."

Last edited by OkiePC; August 31st, 2011 at 01:49 PM.
  Reply With Quote
Old August 31st, 2011, 03:08 PM   #3
gnieport
Member
United States

gnieport is offline
 
Join Date: Nov 2008
Location: Ohio, USA
Posts: 6
I would like to expand on the original machine setup. The machines are isolated; the PV is connected directly to the SLC serial port with an AB serial cable. My hope was to insert the AIC+ in the middle to allow a PC connection for commissioning.

I am able to connect the UIC individually to each device without issue.

Thank you for the suggestion about the driver and harmony files. We will be making another return trip to the client soon, and those changes will be first on my list.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB SLC 5/04 processor error help rjmarinaro LIVE PLC Questions And Answers 27 July 7th, 2008 03:13 PM
connecting SLC 5/04 to Panelview through rs232 Bcon1006 LIVE PLC Questions And Answers 3 March 4th, 2007 09:24 AM
SLC 5/04 + 1747-SN,B passthru to Panelview paperboy4828 LIVE PLC Questions And Answers 2 March 2nd, 2007 02:18 PM
Ab Slc 5/04 Hsce plastics LIVE PLC Questions And Answers 3 January 31st, 2005 03:03 PM
AB CTC units..with 2 SLC 5/04 DH+ Russ LIVE PLC Questions And Answers 4 December 15th, 2004 04:02 PM


All times are GMT -5. The time now is 03:12 PM.


.