Old September 15th, 2011, 07:37 PM   #1
ddeshi2
Member
United States

ddeshi2 is offline
 
Join Date: Dec 2010
Location: Baton Rouge
Posts: 87
1769-IF16C module

Hi all, I'm using a Compactlogix PLC with 1769-L32E processor, 1769-IF16C, 1769-OF8C input and output modules.I'm using RSLOGIX5000 to develop the program. It is a 12-bit system. I'm configuring all the input channels to " scaled for PID". I'm using PID instruction in my program and trying to configure it.My question is what should I enter in the fields of Unscaled Min. and Unscaled Max. for PV. Is it 0-16383 or 0-4095? One of my friends told me that as it is a 12 bit-system and my channels are "scaled for PID" I should enter 0-4095 And if it is a 32-bit system it would be 0-16383. Is he right? Should I enter 0-4095? Please help.

Thank you,

Ding
  Reply With Quote
Old September 15th, 2011, 08:23 PM   #2
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
For the 1769-IF16C refer to Page 42 (PDF 42)of the Manual.

http://literature.rockwellautomation...m018_-en-p.pdf

For the 1769-OF8C refer to Page 4-27 (PDF 109) of the Manual.

http://literature.rockwellautomation...m002_-en-p.pdf

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.
  Reply With Quote
Old September 15th, 2011, 08:44 PM   #3
ddeshi2
Member
United States

ddeshi2 is offline
 
Join Date: Dec 2010
Location: Baton Rouge
Posts: 87
@Sthompson

So, is it 0-16383 even for 12-bit system? Please help

ThankYou!

Ding
  Reply With Quote
Old September 15th, 2011, 08:57 PM   #4
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,725
Quote:
Originally Posted by ddeshi2 View Post
@Sthompson

So, is it 0-16383 even for 12-bit system? Please help

ThankYou!

Ding
Don't get hung up on how many Bits it is, just read the Manual. Allen Bradley should know how it works.

The Table on Page 4-33 (PDF 115) might be a little more helpful for the OF8C.
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message. However, many electrons were terribly inconvenienced.
  Reply With Quote
Old September 16th, 2011, 12:21 AM   #5
zhoudq
Member
China

zhoudq is offline
 
zhoudq's Avatar
 
Join Date: Jul 2011
Location: JiangSu Province
Posts: 51
if it is the 12 bit system, the range is 0--4095, be equal to
2­11
  Reply With Quote
Old September 16th, 2011, 12:28 AM   #6
zhoudq
Member
China

zhoudq is offline
 
zhoudq's Avatar
 
Join Date: Jul 2011
Location: JiangSu Province
Posts: 51
be equal to 2 of 11 powers
  Reply With Quote
Old September 18th, 2011, 07:49 PM   #7
ddeshi2
Member
United States

ddeshi2 is offline
 
Join Date: Dec 2010
Location: Baton Rouge
Posts: 87
@ all

Thank you!

@Zhoudq

I'm trying to scale my readings of the pressure transmitter (4-20 ma to 0-750psi)for displaying on to the HMI. I'm using 1769-IF16C analog module and SCL instruction. What will be my Input Raw Max. and Input Raw Min. values? Will it be 0-4096 or -32767 to 32767? In the manual it was given as -32767 to +32767 but I'm not sure whether it is for 12bit system or not. Can you please help me with it.
Attached Images
File Type: jpg 1769.jpg (52.1 KB, 152 views)
  Reply With Quote
Old September 18th, 2011, 10:21 PM   #8
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,513
Raw data depends on how you have configured the card. Your picture above shows the choices. So how have you configured it? 0-4095 is not one of them.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old September 19th, 2011, 08:42 AM   #9
ddeshi2
Member
United States

ddeshi2 is offline
 
Join Date: Dec 2010
Location: Baton Rouge
Posts: 87
@Mickey

This is not the manual that came with my PLC. I have lost the manual and when I searched online I found this. I don't think it is for a 12bit system. I have a compactlogix 12 bit system. I have configured 4 of my input channels as 4-20ma,60HZ, Raw/Proportional data. I want to display my Pressure transmitter readings (0-750psi) on the HMI and for displaying I need to scale the values. I'm using SCL function block for scaling. What would be my Input Raw Max and Input Raw Min values. Will it be 0-4095 or -32767 to 32767? Please help.

Thank you!
Ding
  Reply With Quote
Old September 19th, 2011, 08:55 AM   #10
fuzzy logic
Member
Italy

fuzzy logic is offline
 
fuzzy logic's Avatar
 
Join Date: Sep 2008
Location: italy
Posts: 291
Agree with sthompson, don't care about the bits !

As you may see in the table you posted, configuring the module as 4-20 mA input and RAW/Proportional data, it will return values using the following considerations:

3,2 mA = -32767
21 mA = 32767

The full range of raw/proportional counts (-32767 to + 32767) applies to the full range, not the normal operating range for an input. While the normal operating range of a 4-20mA current input is 4-20mA, the full range is actually 3.2-21mA. As a result, a 4mA raw/proportional input channel will actually read around -29800, not -32767.

Hope this clears things,

- fuzzy logic
  Reply With Quote
Old September 19th, 2011, 11:30 AM   #11
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,513
See picture below for data format values. I would use the scaled for PID or engineering units myself.
Attached Images
File Type: jpg DataFormat.jpg (65.5 KB, 72 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old September 19th, 2011, 12:40 PM   #12
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,513
See below for a very useful tool for checking the scaling and data values.

Created by John Soltesz

http://www.plctalk.net/qanda/showpos...23&postcount=1
Attached Files
File Type: xls scaling chart.xls (49.5 KB, 41 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb

Last edited by Mickey; September 19th, 2011 at 12:45 PM.
  Reply With Quote
Old September 20th, 2011, 08:48 AM   #13
ddeshi2
Member
United States

ddeshi2 is offline
 
Join Date: Dec 2010
Location: Baton Rouge
Posts: 87
@ all

Thanks for the help.
@ Mickey,fuzzylogic

How did you come up with -29,822 to 29,085. Is it just by following the manual or is there any calculation involved?

Thank you!
Ding
  Reply With Quote
Old September 20th, 2011, 09:48 AM   #14
fuzzy logic
Member
Italy

fuzzy logic is offline
 
fuzzy logic's Avatar
 
Join Date: Sep 2008
Location: italy
Posts: 291
Ding, manual gives you the needed value... anyway you may calculate those values, using a formula.

Here below a scaling formula you may use.
  • In = Input value
  • InRawMax = Maximum attainable input value(21 mA)
  • InRawMin = Minimum attainable input value (3.2 mA)
  • InEUMax = Maximum scaled value(32767)
  • InEUMin = Minimum scaled value(-32767)
Example 1: want to know which value corresponds to 4 mA

(4-3.2)x(65534/17.8)+(-32767)
0.8 x 3681.7 -32767
-29821.64

Example 2: want to know which value corresponds to 20 mA

(20-3.2)x(65534/17.8)+(-32767)
16.8 x 3681.7 -32767
29085.56

- fuzzy logic
Attached Images
File Type: jpg scaling.JPG (6.0 KB, 55 views)

Last edited by fuzzy logic; September 20th, 2011 at 10:19 AM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Analog Input underscale brucechase LIVE PLC Questions And Answers 11 January 3rd, 2007 11:13 AM
1769 OF2 Analog Output Module Thomas Franklin LIVE PLC Questions And Answers 0 November 18th, 2005 08:54 AM
plc5 with AB 1771-DB basic module, its urgent plz help me nileshsurya LIVE PLC Questions And Answers 6 July 20th, 2005 01:45 AM
Philosophy of Equipment Error Recovery, Alarm recovery, and Re-initialization Hester LIVE PLC Questions And Answers 8 May 11th, 2004 07:40 PM
SLC 5/03 data loss andydaoust LIVE PLC Questions And Answers 1 October 10th, 2002 06:38 PM


All times are GMT -5. The time now is 06:53 AM.


.