plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old December 19th, 2011, 09:12 PM   #1
diat150
United States
diat150 is offline
reading 12 volt signal using 0-10 volt analog input
IM trying to find a cheap way to read system voltage using a 0-10 vdc input. my working voltage range is from 10-20 volts. Is there a voltage dividing circuit or something that I can put together that would keep my 10-20vdc working voltage scaled to my 0-10vdc analog input?
Old December 19th, 2011, 10:44 PM   #2
Mickey
United States
Mickey is offline
Mickey's Avatar
See picture and links.
http://www.google.com/search?rlz=1C1...viding+circuit
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old December 19th, 2011, 10:57 PM   #3
danw
United States
danw is offline
danw's Avatar
It's an iffy situation. It's cheap, but it might blow your analog input, because your analog input circuit is likely to 'see' 20 volts, not 10 volts:
You want to see from a 10 volts range which is 10-20 volts with respect to the source's low side. Whether your analog input will do that depends on how much common mode it can tolerate and how high it can float above ground.
A couple of 100k ohm resistors in series will provide a reasonable impedance to the source, and will load your analog input slightly, but scaling can correct for the error.
The problem is that the point labeled a (negative terminal at source) is probably grounded somewhere, so the your analog input will likely see the voltage with respect to ground, not with respect to its own (-) terminal.
Your low side is elevated above the source's negative.
Some AI's can't take much common mode voltage. Some will saturate so the signal looks full scale up or down and not be damaged, but others can be damaged by excessive common mode.
If your analog input is single ended, do not try this.
If your analog input is differential, it might handle it.
Old December 19th, 2011, 11:05 PM   #4
diat150
United States
diat150 is offline
all grounds will be common. I should have mentioned that. The analog input would be on a ge versamax nano
Old December 19th, 2011, 11:40 PM   #5
ndzied1
United States
ndzied1 is offline
ndzied1's Avatar
I was going to recommend the voltage divider as well.
Make sure you test this first with your DMM and make sure to check the common as danw said.
__________________
nOrM
nOrM=Norman Dziedzic Jr.
"I decry the current tendency to seek patents on algorithms. There are better ways to earn a living than to prevent other people from making use of one's contributions to computer science." Donald Knuth
Old December 20th, 2011, 12:38 AM   #6
Mickey
United States
Mickey is offline
Mickey's Avatar
Or use a transmitter. See link below
http://www.api-usa.com/signalconditioners_dc_input.php
__________________
Mickey
Old December 20th, 2011, 04:17 AM   #7
keithkyll
United States
keithkyll is offline
Add 1N4740A (10V, 1W zener) in series. Add .1 uF Monolythic across input for noise. Cathode to +10-20V input. Put Zener in temp stable area to minimize drift. Add another 1N4740A across analog input if you want.
Even the cheapest opamps can take over 30 volts without damage. AD's analog module for the 205 series is rated at absolute max +/- 75 volts. No danger at 20 volts.
Note that this is the cheap way. I would never do it. Too much thermal drift. Use a signal conditioner.
Old December 20th, 2011, 07:45 PM   #8
daba
United Kingdom
daba is offline
daba's Avatar
Mickey's voltage divider circuit in post #2 is totally adequate. The voltage "seen" by the analog input will be one-half of the input voltage (both R's same value), providing the impedance of the analog input is much higher compared to the value of the lower resistor.
I have exactly this arrangement to provide 10V from a 24V supply to my training rig analog input potentiometers, although instead of two individual resistors I used a 20-turn cermet potentiometer, so that I could "trim" the output voltage to exactly 10V.
One advantage of using a potentiometer is that any temperature drift affects both the "upper" and "lower" resistances equally, so my 10V doesn't drift at all.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem
Old December 20th, 2011, 10:39 PM   #9
diat150
United States
diat150 is offline
I will also be just turning the analog input on occasionally. so it wont be on 24-7. maybe an hour or two at most a day.
Old December 21st, 2011, 05:30 AM   #10
shooter
Netherlands
shooter is offline
shooter's Avatar
for daba better use a lm319 for a constant voltage, and diat use max 10 k as the input resistance of the analog port is not very high.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Analog signal with different source of supply flyers LIVE PLC Questions And Answers 7 July 18th, 2011 03:57 AM
p & g signal conditioner to analog input card jimbom LIVE PLC Questions And Answers 0 June 26th, 2009 06:09 AM
S7-200 and analog input problem mniknezhadi LIVE PLC Questions And Answers 3 July 31st, 2008 03:33 AM
Analog signal and DC Drive issue NBJamie99 LIVE PLC Questions And Answers 8 July 13th, 2008 11:55 PM
analog input SIMATIC S7-200, EM235 sarac LIVE PLC Questions And Answers 1 October 26th, 2006 03:32 AM