Hi
I have a powerflex 525 on my desk and a clx plc and have foolowed the AB quickstart procedure
I have added the powerflex and can see it from logix and can create and reset alarms so comms is up
in the quick start it says to set parameter 46 and 47 to Ethernet IP
If I set FreqCommand to 150000 and set Start to 1 nothing happens.
The drive is NOT in fault
Any ideas how to get the drive to go into run
Old May 16th, 2015, 08:45 AM   #2
Plastic
United States
Plastic is offline
150000 seems out of range.
Try entering 6000 for 60.00 hz output frequency
Even though you have intent to run from Ethernet/IP, you still need to jumper Dig Input terminals #1 to #11
The 525 is a Safe-Off drive. On your desk you will need to jumper S+ to S1 and S2.
If you are using the embedded Ethernet port then your settings for command are Ethernet/IP, if you are using the DLR option card, (also Ethernet/IP), you have to set 46 and 47 to aux cummunication
Old May 16th, 2015, 09:10 AM   #3
cjd1965
United Kingdom
cjd1965 is offline
Hi Plastic
That worked ..the link was missing. The speed ref is straight from the AB quick start but I changed it to 2500 (25Hz) and that is what I got.....
Any tips for connecting a thermistor ?
Old February 5th, 2018, 10:13 PM   #4
Boxy
Australia
Boxy is offline
Boxy's Avatar
Pf525
We use external thermistor relays and wire it to a terminal (generally Term3 or 5) and set that as an Aux Fault input.
To use a PF525 with a thermistor directly is terrible.
Essentially you set the voltage input up to drive an output and then use the output to drive a dig input set as Aux Fault.
But to use the voltage input you need resistor and set up a voltage divider.
Waste of time.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
AB PowerFlex 525 + Ethernet AgustinR LIVE PLC Questions And Answers 8 March 10th, 2015 11:49 AM
Powerflex 525 Control Module jayare12 LIVE PLC Questions And Answers 1 January 23rd, 2015 11:41 AM
Powerflex 525 Detecting Loss of ethernet connection DAnderson LIVE PLC Questions And Answers 1 December 29th, 2014 12:30 PM
Ethernet Ip Sensors The Plc Kid LIVE PLC Questions And Answers 6 October 16th, 2009 01:05 PM
IP Addressing and Control Logix gizmo LIVE PLC Questions And Answers 7 February 11th, 2003 10:06 AM