Hi everyone and happy new year y’all.
Have anyone use a 110 Vac instrumentation cable for a 220 Vac device?
Never run 110Vac rated cable on 220Vac!
One of three things will happen:
1. It will catch fire when you commission the device.
2. The insulation will degrade much faster than normal, and in maybe 1 year from now, it will catch fire.
3. The insulation will degrade much faster than normal, and in maybe 1 year from now,you will start to see sporadic false readings from your device. Later it will catch fire.
As this cable is sometimes a twisted pair, I refer to such cable as the twisted firestrter.
Just plowed through Helukabel's catalog. The lowest rated cable I could find was 225V.
Exception were LAN cables, for which there is no insulation rating.
things you must take into consideration.
1. the insulation rating of the wire.
2. the current rating of the wire.
3. the length of the wire (voltage drop).
I have never seen any 110 volt cable with less than 300 volts ac, but then again, there may be some out there.
james
I have some 24VDC contact signals and 115VAC to the coil of a contactor to go to an enclosure. Is there anything wrong with running the 115VAC...
2,144
Hello anyone, i need your helping. coz im building switchboard send to USA with UL label. i could find all component with UL listed but...
3,714
Hello all, To start with I did not do this.....I am the lucky one to figure it out..... With that being said we have an Ozone generation machine...
34
17,785
I am looking for a solution for how to read the presence of a 110 vac signal when the plc I am using only has dc source or sink inputs. I know...
2,566
Hey guys! I'm a newbie in the control area, so I'm gonna drop some thoughts here... We want to control the opening of big silos (about 1900...
1,494