The 1734-IB8 has no hardware counting function correct?
I am trying to find something to substitute in for a 5069-IB16F (since lead times are like June if you believe the lie, and September if you are realistic). So I figured I could do Point IO. (I was also planning on switching all IO to remote IO for this product line anyways so this seems a good excuse to do it.) I don't want to have to have to go to a High Speed counter card as that seems over kill for my application which would see at most 60Hz probably around 30Hz though.
Unless you're considering catching counts during a connection loss, at 30Hz and with an EIP connection, do you really need an onboard counter?
I mean unless my math is off, isn't 30Hz 33mS poll time?, and then wouldn't I need to do half that at the very least to make sure I don't miss any? sounds like 10mS would be safer. But then if I needed to make sure it could handle up to 60Hz I would need a 5mS poll time. Isn't that really pushing it for EIP? I don't think I have ever see anyone in a plant run EIP polling faster than 50mS. But I guess that is PLC to PLC on the Machine network, and not PLC to IO on a local IO network.
If it was EtherCat or something it would probably me no issue.
You are correct that the 1734-IB8 has no onboard counter features. It has a 0.5 ms minimum debounce delay as well.
If you don't want to use an IJ, IK, or VHSC then you could try the 1734-8CFGDLX, which has onboard DeviceLogix that could be used to implement a medium-speed counter.
I was able to count reliably up to about 1000 Hz with a similar CompactBlock I/O module a decade ago, but haven't tested the 1734 module for similar applications. And of course you will need RSNetworx just to get that DeviceLogix editor.
Hello, I don't have enough inputs on my RIO and would like to replace a 1734-IB4 input card with a 1734-IB8. What must I change in the...
1,628
Hi everybody, I have with me the following: 1. 1756-L73S controller + 55L7SP safety partner 2. 1756-ENBT 3. 1756-DNB 3a. 1791DS-IB8XOB8 3b...
2,269
We have a 1734-IB8 card that only has one input landed on it but we keep continually blowing the card up because of that input. Is there something...
2,733
Dear All, I have point IOs 1734-ib8 which is connected by an encoder resolution is 600 only but after using it losses count can any one idea how...
2,336
I need to set the frequency of a pulse output that will be read like a direct input in a 1734-IB8. So, I read the module especifications but I...
3,454