1734-IE2V Analog
Patriot_101
Nov 2018
Indiana
This is probably something I am overlooking however using a 10 k 360 degree pot the analog input card misses the counts... So if I have it set to 5 it might go around 3 or 4 times before it see's it. Any help would be appreciated
welcome to the forum.
please tell us the model # of the pot you are using.
is this a single turn or multi turn pot?
if it's a single turn pot, does it turn continuously or have stops?
if it's a single turn pot, the stops may have been damaged and not working.
if it's a single turn pot, there may be a dead band in it.
lots of questions.
james
Figure out if the problem is on the field side or the program/configuration side. Use a voltmeter to check the voltage at the terminals on the AI module while you rotate the pot. Also make sure you have the wires on the correct terminals.
Not sure what this means. To what do each of the "it"s refer?
Sorry I should of been more descriptive . By it I meant the pot itself. If I turn the pot real slow it will do fine However, as soon as you start to turn the pot a little quicker you can see the analog numbers in the program start skipping digits. If I set the module up for a high of 100 and a low of 0 it will never see the numbers. If I set the module for a high of 10 low of 0 it does better but still cannot rotate the pot to quickly
Thanks again for any and all help
Troubleshooting technical issues remotely requires accurate descriptions of the problem in appropriate terms. "Real slow" and "a little faster" may make perfect sense to you but they're meaningless to me. Is "real slow" one RPM? Is "a little faster" 10 RPM?
There could be two issues at play here. First, the rate at which the AI module refreshes itself. Under the hood, it performs an analog-to-digital conversion. That conversion doesn't happen instantaneously. You'll have to check the documentation for the module to find out how frequently the value inside the PLC gets refreshed.
The other issue is how often RSLogix gets refreshed. It is faster when you are connected to the PLC using an Ethernet connection compared to a serial connection.
Slow would be around 10 rpms. Anything quicker the program does not see.
Basically I have a compare instruction if A<=B then energize the output. A being a setpoint and B coming from the 1734-IE2V.
Thanks again
Hello all, I have attached a video in which the 2 point analog input flashed red for a sec/ The one marked with yellow name sticker.It is scaled...
3,263
Hi All, Just have a quick question would appreciate your advice, I am using a 1734-IE2V AB card on a point IO and connecting a small pressure...
2,328
Hello, I'm using a 1734-IE2V for a load cell. We want to measure between -5Kn to +5Kn. See attached photo. I'm assuming using Voltage Range of...
1,455
I am trying to connect 0-5V humidity sensors to a 1734-IE2V. My readings are all over the place. (fluctuating) I have a 24V to 5V converter to...
1,926
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
63