1734-IE4S Loss of inputs

halla26

Member
Join Date
Jul 2009
Location
england
Posts
69
Hi all.

I'm currently working with a safety guardlogix 1734-ie4s in which it keeps losing its channels i.e. red lights and fault bits.



The card is showing a solid red led for all 4 channels and giving no 24v output suddenly. I've swapped the card with a spare which at first worked, I then lost 2 of the channels for temperature sensors, then after a reboot lost the other two.



Fault tag status are

Channel 0 - 125 - Field I/O power is missing 24V power is not within specification. Check field power supply and wiring.

Channel 1 - 120 - ADC channel config mismatch Dual ADCs are not configured the same. If the problem persists, replace module.

Channel 2 - 125 - Field I/O power is missing 24V power is not within specification. Check field power supply and wiring.

Channel 3 - 125 - Field I/O power is missing 24V power is not within specification. Check field power supply and wiring.



The card is set to internal module power yet giving no 24v out with the above faults active.



Rockwell support isn't getting anywhere much at the moment unfortunately.
 
I don't know how helpful this will be, but it sounds like you have field wiring issues along with incorrect module configuration. Are you using single or dual channel mode? If dual, both inputs need to be high (logical 1) within the set discrepancy time.
 

Similar Topics

I ran into a strange issue the other day. System has been up and running for many months. An analog input channel suddenly reported 0mA. I...
Replies
21
Views
3,357
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
76
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
19
Views
764
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
Replies
3
Views
257
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
362
Back
Top Bottom