i am bench testing a 1734 -VHSC24 Point I/O High Speed counter module,
i cannot find any examples of wiring the outputs from the module.
does anyone have experience with wiring relays to the following?
- output 0 from Module 1 terminal 6 and Module 2 terminal 2
- output 1 from Module 1 terminal 7 and Module 2 terminal 3
You're correct that the documentation could be friendlier. Even the little sketch on the side of the 2nd module is not super clear.
The two Outputs on a 1734-VHSCx are fast (25us ON, 150 us OFF) 24V solid state sourcing outputs. They derive their power from the Field Power Bus of the POINT I/O assembly to their left, and the output can drive a load of up to 0.5A. They have open-circuit and short-circuit detection diagnostics.
The two "RET" terminals on the second module are connected to the DC Common of the field power bus. An output load can be connected between Output 0 or Output 1 and either RET, and it will be energized by +24V when the Output comes on. They are basically just another place to land wires you want to connect to the DC Common of the Field Power Bus.
The Vaux terminals are not connected to the POINT I/O field power bus: they give you a location to provide power for the encoder and terminate the encoder's power wire. The two VAux+ and the two VAux- terminals are just connected together internally.
That is handy for encoders that take 5, 9, 12, or 15 volt power instead of 24.
You can drive a small relay with the output of the VHSCx if you wish; that will give you more power capability but of course less speed.
Hi Ken,
thanks for the detailed reply, i looked everywhere on Rockwell's site for this info and even googled wiring diagrams but could not find any info what so ever, i was hesitant to wing it as did not want to do any damage to the module.
Regards
Alan
Morning Guys, I am installing a turbine flow meter with a pulse output to measure flow on a compactlogix 5069 -L306ER through a 1734-VHSC24...
1,596
Hello to all and thanks for help in advance. I am trying to set up sensors to detect blade RPM of a mower using 2 sensors and a VHSC24 card. I...
1,544
Does anyone know how to set the output window on-off values on the fly without having to inhibit the module? I could of sworn when I first started...
2,383
Hey people! For a school project, I and a friend have a 1734-VHSC24 connected to an encoder. Simultaneously we have 2 x kinetix 5700 with servo...
1,930
Hello, Looking for some examples for the 1734-VHSC24 module. I have a Keyence Self-contained CMOS Laser Sensor LR-ZHB Series wired all up and...
1,142