1746-HSCE (SLC) Encoder program
Is it possible to load in a new number into the encoder everytime I do a soft reset. For example firs SR load in 500 counts then the next SR load in 1000 counts etc..
It will be a lot more efficient to do the math at controller level.
I would write similar ladder logic for 500PPR and 1000PPR and "switch" between recipes when the soft reset is triggered.
Processor Error Message: G file configuration error.. user program G file size exceeds capacity of the module. I cannot seem to find any data...
2,043
I have a double end tennoner with a ball screw for opening and closing. On the back of the motor driven by a VFD there is a 100PPR differential...
3,906
I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
1,029
Hi there, I have a machine where was a servo with extra encoder. That encoder had resolution 100ppr/5V. We did replace complet servopack (...
951
I have a SLC 5/05 processor and I am trying to reference an output from a High speed counter card to be used elsewhere in the PLC. The output...
1,643