1746-NI16I problem - channel 7 not read actual value
jalal
Mar 2008
Kirkuk
Hi There,
I have a 1746-NI16I analogue card. (In the field device I have 5mA and in the channel scaling ladder it measures zero value. Just channel 7 is not work properly the other channels are well.
Please, attached is full description for this problem.
If anyone could help I would be most grateful.
Jalal_Iraq
Is this a new install or has it been working then stopped? It could be wiring or a program issue. We can't see what you see or know what you know. Very hard to solve wiring problems over the internet, if you zip your .RSS file and post it here someone can take a look for code issues.
It is not new install, it was working properly then this problem happened, I checked the loop wiring, it is ok, the signal reads 5 mA, 25Vdc
Below is the Config. word
15 14 13 12 11 10 9 8 7 6 5 4 3 2 1 0
1 0 1 1 0 0 0 1 0 0 0 1 0 0 0 0
Good morning Mickey,
Good news
I went to the O:1.7 bit 8 it was 1 , I changed to 0 and it works properly,
in HMI it read 3.9 Bar ,which is same actual value on the transmitter.
We did it again (solve problems).
Thanks All
jalal
Hii, in the user manual for the 1746-NI16I AI card, publication 1746-um001_-en-p.pdf on page 7-21 it gives an example of using these cards in...
2,092
Hello everyone, I'm working on a converting SLC to ControlLogix project. I have a question about 1746-NI16I card. The AI card is Class 3...
1,792
Looking at setting up a 1746-NI16I class 3, I'm looking at the channel configuration word and have a few questions. Do I ignor bits 0,1 & 2 as...
2,005
I have searched a bit and studied the users guide and I think I am close, but I must be missing something stupid. This is my first PLC experience...
37
6,538
I've got to use a 1746-NI16I in a remote I/O chassis. Is there anywhere I can download the class 1 sample code that's shown in the user manual...
1,712