1746-OW16 connection issue using 1747-AENTR
JBooth
Oct 2013
Palmetto, Ga
70
I am looking to replace a SLC5/05 processor with an AENTR adapter. Configured the rack in a compactlogix. The connection to all of the cards in the local rack and expansion rack are working perfectly with the exception of the 5 1746-OW16 output cards. Those just show a connection fault. Did a module discovery and the cards show up there, exactly as I configured them. Has anyone here run into a similar issue?
What firmware revision is your 1747-AENTR ?
How many total slots are in the chassis + expansion ?
What slots are the 1746-OW16 modules in (and are they the right-most slot numbers) ?
How many total connections do you have to the CompactLogix over EtherNet/IP and what model of CompactLogix is it ? Connecting to each module directly (the only way the -AENTR works, to my understanding) could use up I/O connections on a small CPU in a hurry.
What is the connection error code ?
I'm thinking this could be a module ID problem, where you would have to manually put in the module ID instead of using auto-detect or selecting the part number, or it could be a capacity problem in the 1747-AENTR.
I'll have to look up the specifics but I know the first releases of -AENTR firmware didn't support the full 30 slot capacity of the 1746 chassis platform the way a CPU or a 1747-ASB does.
Dis is nutsen! Meesa think more inputs, how wude!
AENTR ar rev 2.003, 20 total slots (13+7), s1 empty, s2-8 IA16, s9 OV16, s10 empty, s11 OW16, s12 BAS, s13-16 OW16, s17-18 empty, s20 NO4I. 1769-L33, 15 CIP connections observed max, 2 TCP connections observed max. Error code is 16#0204 connection request error.
After some more playing around, I've gotten some mixed results. All of the current OW16 cards are series C. I put a series D OW16 in s17, and it connects fine. Did see something about AENTR not supporting partial I/o, so moved series C card from s11 to S10, put series D card in s11, and moved NO4I to s17. In that configuration, connect to the series C in S10, series D in s11, but not the series C in s13-16. All other cards connect.
Scrounged up more cards and filled the rack, ib16/C in s1, IA16/C s2-8, OV16/C s9, OW16/c s10-11, bas/C s12, OW16/c s13-16, OW16/D s17-18, no4i s19. Connects to everything except series C OW16 in s13-16... Put OW16/D card in s12-13, moved bas to s18, still not seeing s13-16. Don't believe it is a backplane issue, since all cards still function with 5/05.
Can't take credit for this, a friend had seen it. But Rockwell, etc. were all lost. Relay output card. Large rack. LOTS of outputs. Output...
1,466
I have two output cards sitting next to each other in a rack: 1746-OW16 1746-OW16 (Octal) output 13 in the first card triggers a solenoid. When...
2,207
Good day all, I would like to know if any of you folks that sell AB parts might have a 1746-OW16 Relay module? As always, I try to support you...
1,219
I have an AB relay module (1746-OW16) controlling a PowerFlex 4 drive, that in turn is powering a conveyor. There are actually many conveyors at...
5,082
HI all, I got some great help my last post here I hope this one goes as well. I am having a problem getting a Banner light to turn on. The light...
4,719