I have the above card series D in a 10 slot rack. Oddly enough every so often it seems to lose its connection to the main trunk on DH+. The RIO(channel B) still seems to function but the only way to get this functioning again is by recycling power to the processor.
Has anyone run into this problem or know of a fix that might alleviate it?
I've found that the DHRIO is EXTREMELY picky about having the proper terminating resistor installed - especially if the DHRIO is located at the physical END of the blue hose ... other DH+ stations (PLC-5, SLC-5/04, etc. don't seem to be so fussy) ...
specifically, sometimes I've plugged a PCMK cable into a DHRIO (8-pin mini-DIN plug) and couldn't communicate - UNTIL I installed a spare 3-pin plug with a resistor on it ... in other words, if the PCMK cable was the ONLY connection to the module, I couldn't communicate reliably without providing the termination resistor ... I've never had a PLC-5 or SLC-5/04 act that way with a PCMK cable ...
so ... have you checked the resistors lately? ...
Hi All; I am having a problem with RSLinx Classic seeing a DH+ network. We have a CLX processor with 2 (slot 5 and slot 6) 1756-DHRIO cards set up...
3,826
Hi all, I have problem on my DHRIO connection between ControlLogix5000 and SLC5/04.I found the DHRIO installed is have a higher revision than the...
2,577
How do I set up channel A on this module to communicate DH+ at 230.4k? Seems dip switch 1 set on 3 is invalid? Any help is appreciated. Kyle
3,817
I'm trying to get a 1791r 8b8p to communicate with a 1756 DHRIO card. Both channel A and B on the DHRIO card are set to RIO. I have a 150 ohm...
6,247
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
430