Has anyone tried this configuration shown in the Allen-Bradley knowledgebase document below.
I have done exactly what the knowledgebase document says, except i am using a controlnet driver instead of ethernet for going online onto the controllogix processor, but no success.
I can see the KF2 module in RSLinx, there is no error in the message instruction. But I just can't write a value from the contollogix processor into the PLC5. Don't understand what I am doing wrong.
I'd really appreciate some help from the experts. Thanks.
Here's the link to the AB knowledgebase document:
http://domino.automation.rockwell.c...54537F24504C8EF285256C3900450922?OpenDocument
I would expect there to be an error in the MSG instruction if it's not working, except if it's simply timing out.
Try disconnecting the 1770-KF2 from the PLC-5 and see if the MSG instruction fails with error then.
Try also observing the COMM light on the PLC-5 when somebody manually triggers the MSG instruction, to determine if the message is making it as far as the PLC-5 serial port.
Post the configuration of your MSG instruction, too. Maybe somebody has this combination of products and can see where you've overlooked something.
Thanks Ken.
It was a silly mistake of the baud rates on the KF2 and the PLC5 serial port not matching.
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
426
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
3,383
:banghead: Remote I/O The occasional times i have had to deal with blue hose/PLC5 I/O addressing it always wrecks my head. Now i am working on...
3,294
Called to a site and am neck deep currently ;) running, but issues. Phase 2 completion has been running for almost 2 years no issues. Controller...
1,639
Hello all. I have a job to add a 1794-IE8 Card in slot 5 on an existing Flex IO Rack which uses a 1794-ASB communications module, which...
3,011