Hello everyone,
I've been having trouble viewing my ENBT card from a remote location despite me entering the correct IP address and subnet. I can connect via 232 with no issues whatsoever and can even see another 1756 ENBT on the same network with a different subnet. I can communicate with the intended ENBT card by pinging it or entering the IP but no matter what I try, it doesn't show up in RSWho as an option. I updated the revision to 4.08 and still cannot see anything. It's really been confusing me as even when I change my static IP to the correct subnet and gateway there doesn't seem to be any viewing at all.
Does anybody have some insight on this? I'm stuck here without a paddle now at this point.
Thank you,
-Jeff
What's your IP and subnet, the PLC's IP and subnet?
Are you using Ethernet or Ethernet/IP driver in RSlinx?
If you are using EIP driver, try Ethernet Device instead and type in the IP address.
my IP is 10.6.0.131, the PLC is 10.6.0.11
both subnets are 255.255.255.0
I'll give that a shot right now but recently the "Host name" has been throwing me off a bit
oh wow... it worked. I feel dumb but thank you haha such a big oversight
I guess it really helps to cover all your bases but thanks for that needed push
You're probably using a VPN over the Internet, and the RSLinx "EtherNet/IP" driver uses a broadcast packet for browsing that will not pass through a VPN connection.
The older "Ethernet Devices" driver doesn't broadcast, which is why it requires you to enter the IP address. That's also why it can use a VPN network connection.
Thank you for explaining it, it's funny how such a simple fix can seem so unobvious until immediately after.
Thank you guys!
The EIP driver will work over VPN as long as you pass it through a GRE tunnel.
Allen Bradley Control Logix 5561 Series Model 1756-L61 Series B Controller. Panel View Plus 1000 HMI Touch Screen. Communication Module 1756 ENBT...
4,602
Hi everybody, following the tip of Ken Roach, i'm opening a new thread to my problem. I have a redundant PLC system, each chassis have two...
7,945
I configured Ethernet module with BOOTP/DHCP . I follow the Ethernet's manual. After Add to Relation List ,i press disable BOOTP/DHCP but no effect.
2,211
please using the usb can i assign any ip address that i want ?
151
Hi, I want to exchange data between two L55 PLCs using ENBT PLC1 is the main PLC and consist of 1756- CNB, L55 CPU and ENBT. Five remote I/O racks...
1,034