Hi all,
We tried to setup the hardware onto a 10 slot rack as follows,
PS
Slot 0: 5580 controller
Slot 1: Safety Partner
Slot 2: Safe Inp
Slot 3: Safe Out
Slot 4: Network comms card
Slot 5-9 empty

So here's the issue we've been getting.
All parts are out of box.
Safety output card has a solid green OK and we're able to read the module info and reset ownership.
Safety input card has flashing orange and green OK. And can't get module info or reset ownership.
Tried different slots but no luck.

Can someone please she'd some light on the issue.?

Tia
 
Card must go in the slot you set up for it in the hardware tree???
Are the inputs configured in the module?
Is your safety network number consistent? (Not sure if that's a thing for local I/O)
DO YOU HAVE an error mesage and code in the module properties?
 
Manual does not list "flashing orange/green"
It does say that "flashing red/green" means you must commission the Unique Node Identification Number.
Does the yellow yield sign show by the module in the hardware tree?
Fun Fun Rockwell.
 
Manual does not list "flashing orange/green"
It does say that "flashing red/green" means you must commission the Unique Node Identification Number.
Does the yellow yield sign show by the module in the hardware tree?
Fun Fun Rockwell.

Yes that's what's happening. How do we commission the UNID number.?
 
"For a backplane port, an SNN is assigned to the backplane and the node
address is the slot number of the device."
" each subnet is assigned a unique Safety
Network Number (SNN), and the UNID is created from the SNN + the
Node Address. "
"CIP Safety I/O modules retain their UNID (SNN + Node) once it has been
assigned, and must be reset before they can be reused with another value."
Publication 1756-RM012D-EN-P - August 2020
Safety Reference Manual
I'm just reading... Hope it helps...
 
Like I asked before, is your safety network number consistent?
You can find this number in the safety processor properties, I think.
Or the Output module properties.
Then enter or paste into the Input module properties.
Reset the module first, I think.
 
Last edited:
I haven't run into this UNID thing before, but I think it basically just means you need the SNN to match the Safety PLC and other modules. And reset the module if you change slots. Prolly a new-out-of-the-box module would create its own setup when it is configured, but this one had issues.
 
I haven't run into this UNID thing before, but I think it basically just means you need the SNN to match the Safety PLC and other modules. And reset the module if you change slots. Prolly a new-out-of-the-box module would create its own setup when it is configured, but this one had issues.

Yes we have come to the conclusion it's a dodgy card.
We got swapped it from one slot to the other, it works for 10 seconds with solid green OK and then gets lost in communication timeout errors.
We're organising a replacement part.
 

Similar Topics

Hey Guys, I thought I knew the answer to this, but after some looking I am starting to doubt myself. I thought the 1756-EN2TR would allow you to...
Replies
2
Views
33
We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
Replies
3
Views
73
We are in the process of converting our plants from PLC5 controllers and 1771 I/O into ControlLogix PLCs and Logix I/O. Up until now we used 1756...
Replies
1
Views
70
Hello all, I have a 1756-EN2TR dual-port Ethernet IP Module attached to my 1756-L73 PLC. I currently have hazard symbols over both the top and...
Replies
9
Views
160
Hi all I have a ControlLogix 1756-L71SP that i want to use for general PLC applications, not safety. I am running Studio5000 v33, i can't...
Replies
2
Views
106
Back
Top Bottom