I would like a sanity check on an application i am working on.
I have a proximity switch counting pulses with a Mark/space ratio of 1:1 on a rotating shaft. 1 pulse per revolution.
the prox is fed into a 1734-IB8 point I/O with an RPI set for 20ms. the CPU is a 1756-L72S with Safety Partner
I am loosing pulses when I go above approx 290rpm (290 PPM) so that is about 5hz. the filter on/off time setting on the module is at default (1m/s from memory)
maximum speed of shaft I am expecting is about 340RPM ( or less than 6 Hz) so I am close to what I require.
I am using a counter to get the pulse rate every 15 seconds then dumping that value into a register then resetting counter. and multiplying the register value by 4 for a rate/minute. the application is to compare head roller speed of a conveyor to the tail roller speed to check for slippage hence the 15 second sampling, I need to alarm & shut-down to save mechanical issues on belt if slippage or a jam up occurs.
should I be looking at a periodic task specifically for this subroutine or any other things i should be aware of?
the combined pulse falling and rising edges should be coming in no faster than 680edge/minute, which is around 85-90ms per edge at 340RPM, so 20ms RPI seems like it should be good enough. If it is not, I would work to solve that problem first.
If it is not solvable, then what speed resolution is required? A hardware circuit to divide the number of pulses by 2 would double the time between edges, but also double the aliasing of the measurement from around 1%+ (85 pulses per count at 340RPM) to 2%+, and more at slower speeds.
Many Thanks i will speed up the RPI and see what effect it has at first opportunity
Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
1,119
Hey Members, I hope all of you are doing well , I am using a 1756-l72 redundancy system, communicating RIO on DLR network. When both my PLC are...
2,466
Hello all.... I am not asking you to fix my issue just a little guidance is all i am asking. I just started with a new company and I am working...
2,621
1752-L72S ControlLogix Controller. I've been asked to store data on recipes. It will be a simple cumulative weight for each recipe which may...
1,175
just need to convince myself what I am doing is OK. Have a project where I am splitting up the process into two 1756-L72 CPUs on an A10 rack. I...
3,526