1756-l72 controllogix redundancy
Rahul3005
Dec 2017
Mumbai
34
Hey Members,
I hope all of you are doing well , I am using a 1756-l72 redundancy system, communicating RIO on DLR network.
When both my PLC are powered on , my system works flawlessly when I initiate a switchover from RM2 module , everything works ok.
When I turnoff my primary rack , my SYNC will become Primary , which is once again working as expected.
The issue is when the primary rack is powered off , I get IO's not responding.
I have set 1756-EN2TR on both redundant chassis as "RING SUPERVISOR".
Is this normal for a DLR network , or am i missing something ? o_O
Thank you for posting the system architecture and those details about the configuration !
The most likely issue is the DLR Supervisor configuration.
Rockwell Automation Application Technique document ENET-AT007 describes the recommended configuration of 1756-EN2T modules in a Redundancy system with DLR.
The Supervisor Precedence value determines which device will be the Active Supervisor. You should configure at least one Supervisor-capable node outside of the redundant CPU chassis pair.
You may also configure Supervisor-capable nodes (with lower Precedence values) in addition, if you wish.
Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
1,053
hi all, I have a customer who has a A-B PLC 1756-L72 (ControlLogix 5572) Controller. He support only Ethernet but my device can only go...
2,237
Hi all. I am working with 1756-L72 processor in a redundant pair chassis. The publication ControlLogix Enhanced Redundancy System, Revision...
7,959
I would like a sanity check on an application i am working on. I have a proximity switch counting pulses with a Mark/space ratio of 1:1 on a...
1,878
Hello all.... I am not asking you to fix my issue just a little guidance is all i am asking. I just started with a new company and I am working...